Re: [EnergyPlus_Support] Multiplier (GetHT Subsurface Data Warning Message))



Another limitation in using a multiplier for window sub-surfaces is the 
impact on daylighting calculations.  Since EnergyPlus does not know 
where each of the individual windows is located, it cannot properly 
calculate the visible light transmitted through these windows into a space.

Rob Hitchcock
=========
teomj23 wrote:

> Dear all,
>
> do you know what are the effects of the use of multiplier in Sub
> Surfaces?
> I would be sure that using the multiplier function of E+, I don't lose
> or compromise important data or features about both the effects of
> solar radiation on windows (heat gain or loss, direct beam solar
> transmittance and reflectance, internal surface temperatures, ecc...)
> and the Building energetic consumptions, due to an incorrect behaviour
> of glazing surfaces in respect to sun path.
>
> Infact in the exported E+ drawing file I have only 1 window of the
> group, while in the editor I have the correct multiplier.
>
> kindly
>
> Matteo
>
> 
> Messages in this topic 
> <http://groups.yahoo.com/group/EnergyPlus_Support/message/7349;_ylc=X3oDMTM0MGo1dTdyBF9TAzk3MzU5NzE0BGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BG1zZ0lkAzczNDkEc2VjA2Z0cgRzbGsDdnRwYwRzdGltZQMxMTY0Mjc3MzgzBHRwY0lkAzczNDk-> 
> (1) Reply (via web post) 
> <http://groups.yahoo.com/group/EnergyPlus_Support/post;_ylc=X3oDMTJwZjV1aG90BF9TAzk3MzU5NzE0BGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BG1zZ0lkAzczNDkEc2VjA2Z0cgRzbGsDcnBseQRzdGltZQMxMTY0Mjc3Mzgz?act=reply&messageNum=7349> 
> | Start a new topic 
> <http://groups.yahoo.com/group/EnergyPlus_Support/post;_ylc=X3oDMTJlZ3FzMTlpBF9TAzk3MzU5NzE0BGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwNmdHIEc2xrA250cGMEc3RpbWUDMTE2NDI3NzM4Mw--> 
>
> Messages 
> <http://groups.yahoo.com/group/EnergyPlus_Support/messages;_ylc=X3oDMTJldWp2a2QzBF9TAzk3MzU5NzE0BGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwNmdHIEc2xrA21zZ3MEc3RpbWUDMTE2NDI3NzM4Mw--> 
> | Files 
> <http://groups.yahoo.com/group/EnergyPlus_Support/files;_ylc=X3oDMTJmcGdoczA0BF9TAzk3MzU5NzE0BGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwNmdHIEc2xrA2ZpbGVzBHN0aW1lAzExNjQyNzczODM-> 
> | Photos 
> <http://groups.yahoo.com/group/EnergyPlus_Support/photos;_ylc=X3oDMTJlN3I2YWEzBF9TAzk3MzU5NzE0BGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwNmdHIEc2xrA3Bob3QEc3RpbWUDMTE2NDI3NzM4Mw--> 
> | Members 
> <http://groups.yahoo.com/group/EnergyPlus_Support/members;_ylc=X3oDMTJlYjMwYnF2BF9TAzk3MzU5NzE0BGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwNmdHIEc2xrA21icnMEc3RpbWUDMTE2NDI3NzM4Mw--> 
> | Calendar 
> <http://groups.yahoo.com/group/EnergyPlus_Support/calendar;_ylc=X3oDMTJkcW42NWs2BF9TAzk3MzU5NzE0BGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwNmdHIEc2xrA2NhbARzdGltZQMxMTY0Mjc3Mzgz> 
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the 
> appropriate folder in the Files area of the Support Web Site.
>
> EnergyPlus Documentation is searchable.  Open EPlusMainMenu.idf and 
> press the "search" button.
> Yahoo! Groups 
> <http://groups.yahoo.com/;_ylc=X3oDMTJkcnFoMzFsBF9TAzk3MzU5NzE0BGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwNmdHIEc2xrA2dmcARzdGltZQMxMTY0Mjc3Mzgz> 
>
> Change settings via the Web 
> <http://groups.yahoo.com/group/EnergyPlus_Support/join;_ylc=X3oDMTJmNWQ1MmFhBF9TAzk3MzU5NzE0BGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwNmdHIEc2xrA3N0bmdzBHN0aW1lAzExNjQyNzczODM-> 
> (Yahoo! ID required)
> Change settings via email: Switch delivery to Daily Digest 
> <mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx?subject=Email%20Delivery:%20Digest> 
> | Switch format to Traditional 
> <mailto:EnergyPlus_Support-traditional@xxxxxxxxxxxxxxx?subject=Change%20Delivery%20Format:%20Traditional> 
>
> Visit Your Group 
> <http://groups.yahoo.com/group/EnergyPlus_Support;_ylc=X3oDMTJka292bXNjBF9TAzk3MzU5NzE0BGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwNmdHIEc2xrA2hwZgRzdGltZQMxMTY0Mjc3Mzgz> 
> | Yahoo! Groups Terms of Use <http://docs.yahoo.com/info/terms/> | 
> Unsubscribe 
> <mailto:EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx?subject=>
> Recent Activity
>
>    *
>        6
>       New Members
>       <http://groups.yahoo.com/group/EnergyPlus_Support/members;_ylc=X3oDMTJmdmk0MzI1BF9TAzk3MzU5NzE0BGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwN2dGwEc2xrA3ZtYnJzBHN0aW1lAzExNjQyNzczODM->
>    *
>        9
>       New Files
>       <http://groups.yahoo.com/group/EnergyPlus_Support/files;_ylc=X3oDMTJnY2Q4ajlsBF9TAzk3MzU5NzE0BGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwN2dGwEc2xrA3ZmaWxlcwRzdGltZQMxMTY0Mjc3Mzgz>
>
> Visit Your Group 
> <http://groups.yahoo.com/group/EnergyPlus_Support;_ylc=X3oDMTJlMGlsNDczBF9TAzk3MzU5NzE0BGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwN2dGwEc2xrA3ZnaHAEc3RpbWUDMTE2NDI3NzM4Mw--> 
>
> SPONSORED LINKS
>
>     * Cad software program
>       <http://groups.yahoo.com/gads;_ylc=X3oDMTJjZjg3YzhiBF9TAzk3MzU5NzE0BF9wAzEEZ3JwSWQDMzM4NzQ4OARncnBzcElkAzE3MDUwMDczODkEc2VjA3NsbW9kBHN0aW1lAzExNjQyNzczODQ-?t=ms&k=Cad+software+program&w1=Cad+software+program&w2=Email+software+program&w3=Wedding+program+software&w4=Medical+software+program&w5=Backup+software+program&c=5&s=143&g=2&.sig=jtVUkkzyD91emWHBkjSeOA>
>     * Email software program
>       <http://groups.yahoo.com/gads;_ylc=X3oDMTJjYmYzNWZlBF9TAzk3MzU5NzE0BF9wAzIEZ3JwSWQDMzM4NzQ4OARncnBzcElkAzE3MDUwMDczODkEc2VjA3NsbW9kBHN0aW1lAzExNjQyNzczODQ-?t=ms&k=Email+software+program&w1=Cad+software+program&w2=Email+software+program&w3=Wedding+program+software&w4=Medical+software+program&w5=Backup+software+program&c=5&s=143&g=2&.sig=vUpU0Py7K3WVwgCZWKLe3Q>
>     * Wedding program software
>       <http://groups.yahoo.com/gads;_ylc=X3oDMTJjM2twN3FvBF9TAzk3MzU5NzE0BF9wAzMEZ3JwSWQDMzM4NzQ4OARncnBzcElkAzE3MDUwMDczODkEc2VjA3NsbW9kBHN0aW1lAzExNjQyNzczODQ-?t=ms&k=Wedding+program+software&w1=Cad+software+program&w2=Email+software+program&w3=Wedding+program+software&w4=Medical+software+program&w5=Backup+software+program&c=5&s=143&g=2&.sig=psNMUzIWO66gnvznvxv_Nw>
>     * Medical software program
>       <http://groups.yahoo.com/gads;_ylc=X3oDMTJjaWZrMmQyBF9TAzk3MzU5NzE0BF9wAzQEZ3JwSWQDMzM4NzQ4OARncnBzcElkAzE3MDUwMDczODkEc2VjA3NsbW9kBHN0aW1lAzExNjQyNzczODQ-?t=ms&k=Medical+software+program&w1=Cad+software+program&w2=Email+software+program&w3=Wedding+program+software&w4=Medical+software+program&w5=Backup+software+program&c=5&s=143&g=2&.sig=pQryPFksl51oSwr3SkdlGg>
>     * Backup software program
>       <http://groups.yahoo.com/gads;_ylc=X3oDMTJjazFuZWNkBF9TAzk3MzU5NzE0BF9wAzUEZ3JwSWQDMzM4NzQ4OARncnBzcElkAzE3MDUwMDczODkEc2VjA3NsbW9kBHN0aW1lAzExNjQyNzczODQ-?t=ms&k=Backup+software+program&w1=Cad+software+program&w2=Email+software+program&w3=Wedding+program+software&w4=Medical+software+program&w5=Backup+software+program&c=5&s=143&g=2&.sig=sTsqpESdbH40EvZgH3Ji5A>
>
> Yahoo! TV
>
> "The 9" 
> <http://us.ard.yahoo.com/SIG=12h1j6ivo/M=493064.8985665.9759897.8674578/D=groups/S=1705007389:NC/Y=YAHOO/EXP=1164284584/A=3848429/R=0/SIG=10lh6opha/*http://9.yahoo.com/>
>
> Daily count down
>
> of top Web finds.
>
> Business News
>
> Hot Headlines 
> <http://us.ard.yahoo.com/SIG=12i1vu527/M=493064.9337501.10154278.8674578/D=groups/S=1705007389:NC/Y=YAHOO/EXP=1164284584/A=4025325/R=0/SIG=12a352npd/*http://us.rd.yahoo.com/evt=44092/*http://smallbusiness.yahoo.com/r-index>
>
> Get localized news
>
> for your area.
>
> Search Ads
>
> Get new customers. 
> <http://us.ard.yahoo.com/SIG=12huibs2n/M=493064.8985663.9760769.8674578/D=groups/S=1705007389:NC/Y=YAHOO/EXP=1164284584/A=3848641/R=0/SIG=1312g85fq/*http://searchmarketing.yahoo.com/arp/srchv2.php?o=US2003&cmp=Yahoo&ctv=Groups2&s=Y&s2=&s3=&b=50>
>
> List your web site
>
> in Yahoo! Search.
>
> .
>



[Non-text portions of this message have been removed]



The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.idf and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/