The outside face environment of the roof should be OtherZoneSurface, because 
there is conditioned space above this zone, correct?

Setting the outside face environment to "ground" simply applies the current 
month's value from GROUND TEMPERATURES to the outside face of the wall or 
floor.  Check the values input for GROUND TEMPERATURES, they may be too low.

Mike



On 9 Dec 2006 at 14:47, dreamerfish8146 wrote:

> Dear all:
>     I try to get the Purchased Air Total Cooling Rate[W] of the 
> underground floor.I set the OutsideFaceEnvironment of the walls, floor 
> and roof to Ground.The other input parameters are the same as 
> overground floors.Then the output Purchased Air Total Cooling Rate[W] 
> all the year is zero.But the Purchased Air Heating Rate[W] is not all 
> zero.I hope I can get help from you in order to amend the input file 
> and get the right result.Thanks a lot!
> 
> 
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
> 
> EnergyPlus Documentation is searchable.  Open EPlusMainMenu.idf and press the
> "search" button.
>  
> Yahoo! Groups Links
> 
> 
> 
> 
> 


========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support      
EnergyPlus-Support@xxxxxxxx





The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.idf and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/