Re: [EnergyPlus_Support] about the fresh air



Yes, it should.  You can confirm this by making a second input file with zero 
outside air.  Then compare the autosized chiller capacity reported in the eio 
output file.  Note that if you have more than one chiller, EnergyPlus 
autosizing sizes all chillers to meet the full load.  You must assign hard 
sizes (just for the chillers) to split the load between multiple chillers.

Mike


On 12 Dec 2006 at 2:46, dreamerfish8146 wrote:

> Dear all: 
>      The system is fan coil and fresh air. I set the outside air flow 
> per person in the zone sizing.I use chillers give the chilled water.I 
> wondered if the cooling capacity and energy consumption of the chiller 
> include the capacity and energy that the fresh air need.If not, how can 
> I get the cooling capacity and energy the outside air need when 
> conditioned to the supply temp?
>     Thanks a lot!
> 
> 
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
> 
> EnergyPlus Documentation is searchable.  Open EPlusMainMenu.idf and press the
> "search" button.
>  
> Yahoo! Groups Links
> 
> 
> 
> 
> 


========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support      
EnergyPlus-Support@xxxxxxxx





The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.idf and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/