The sizing of the fan coil's cooling coil chilled water flow rate takes 
into account the
ventilation air. That the chiller size will have built in the capacity 
necessary to meet
the cooling load including fresh air. During the simulation the fan coil 
will act to meet
its total load: zone cooling and outside air. This load will be passed 
to the chiller through
the chilled water loop so the chiller will also meet the total load.

Fred Buhl

dreamerfish8146 wrote:
> Dear all: 
>      The system is fan coil and fresh air. I set the outside air flow 
> per person in the zone sizing.I use chillers give the chilled water.I 
> wondered if the cooling capacity and energy consumption of the chiller 
> include the capacity and energy that the fresh air need.If not, how can 
> I get the cooling capacity and energy the outside air need when 
> conditioned to the supply temp?
>     Thanks a lot!
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
>
> EnergyPlus Documentation is searchable.  Open EPlusMainMenu.idf and press the "search" button.
>  
> Yahoo! Groups Links
>
>
>
>   


The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.idf and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/