The problem was in the COIL:Water:Cooling=2E The ?Design Inlet Air Humidity
Ratio? was smaller than the ?Design Outlet Air Humidity Ratio? witch is
physically impossible=2E It seems that under this situation the cooling coil
was disabled without any warning or severe error=2E I would suggest a warning
under this situation=2E
Miguel Angel Pascual
_____
De: EnergyPlus_Support@yahoogroups=2Ecom
[mailto:EnergyPlus_Support@yahoogroups=2Ecom] En nombre de Pedro Rodrigo
Enviado el: viernes, 15 de diciembre de 2006 17:21
Para: Foro ENERGYPLUS
Asunto: [EnergyPlus_Support] Problems with fancoil simulations
Thank you Michael for your suggestions=2E
I have monitored coil operation with the report variables "Total Water
Heating Coil Rate" and "Total Water Cooling Coil Rate"=2E In a winter
simulation, when the system starts up (Monday, 8:00 AM) there is a quick
rise of heatring coil energy and afterwards energy returns to zero and
continues zero the entire simulation=2E The same energy curve occurs in a
summer simulation for the cooling coil rate=2E
Do you know how to explain this effect?
(I have changed thermostat controls to dual setpoint with deadband and the
same results were obtained)=2E
Pedro Manuel Rodrigo Cruz
Universidad de Jaén
Michael J=2E Witte wrote:
Thank you to Miguel for offering to review the input file=2E I have two
suggestions:
1=2E Be sure to read the definition of "Zone/Sys sensible heating rate" and
"Zone/Sys sensible cooling rate" in the Input Output Reference=2E If the fan
coils have outside air flow, "Zone/Sys sensible cooling rate" may not always
mean that the cooling coil is operating, it may just be cold outside air
flowing into the zone=2E Note that fan coils in EnergyPlus run with continuous
fan whenever the unit is scheduled on=2E Add these report variables to monitor
coil operation:
Total Water Heating Coil Energy
Total Water Cooling Coil Energy
2=2E In version 1=2E4, changes were made to the fan coil unit controls to
provide
better control at low load conditions when the outside air may need to be
tempered=2E These controls rely on knowing both a heating and cooling
setpoint=2E
I would recommend trying the dual setpoint with deadband thermostat controls
and let the heating and cooling coil schedules control the availability=2E
Mike
On 11 Dec 2006 at 19:34, Pedro Rodrigo wrote:
> Hi all:
> I´m trying to model a two=2Dpipe fancoil system in a mono=2Dzone building
model=2E
> I´m using the "fancoilautosize" example as a reference=2E
> The "fancoilautosize" example uses a "fancoil unit:4 pipe" object, a
chilled
> water loop linked to the cooling coil and a hot water loop linked to the
> heating coil=2E I´m trying to modify the availability schedules in order to
> supply heating only in winter season and cooling only in summer season
> (cooling coil and chilled water loop must be off in winter =2D heating coil
and
> hot water loop must be off in summer)=2E
> I have launched weather file simulations and results reported in the
variables
> "Zone/Sys sensible heating rate" and "Zone/Sys sensible cooling rate" show
> that the system is supplying heating and cooling in both summer and winter
> seasons=2E The zone temperature (variable "Zone mean air temperature" ) does
not
> follow the zone setpoints=2E
> The following schedules have been used in my simulations:
> =2D FanAndCoilAvailSche d uses the same scheme for the hole year: it is ON
from
> 8:00 AM to 9:00 PM (Monday to Friday) and OFF on weekend=2E The same
schedule is
> used for the objects "fancoil unit:4 pipe", "fan:simple: const volume",
> "coil:water: cooling" and "coil:water: simpleHeating" =2E
> =2D The Zone Control Type Sched is set to 1 in winter season (single heating
> setpoint) and 2 in summer season (single cooling setpoint)=2E It is used in
the
> "zone control: thermostatic" object=2E
> =2D The chilled water loop operation scheme uses an Availability Schedule
that
> is OFF in winter season and ON in summer season=2E
> =2D The hot water loop operation scheme uses an Availability Schedule that
is ON
> in winter season and OFF in summer season=2E
> Does anybody know where is the problem?
>
>
> Pedro Manuel Rodrigo Cruz
> Universidad de Jaén
______________________________________________
LLama Gratis a cualquier PC del Mundo=2E
Llamadas a fijos y móviles desde 1 céntimo por minuto=2E
http://es=2Evoice=2E <http://es=2Evoice=2Eyahoo=2Ecom> yahoo=2Ecom
__=2E_,_=2E___
Messages
<http://groups=2Eyahoo=2Ecom/group/EnergyPlus_Support/message/7448;_ylc=3DX3oDMTM0
MmhiNW5yBF9TAzk3MzU5NzE0BGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BG1zZ0lk
Azc0OTgEc2VjA2Z0cgRzbGsDdnRwYwRzdGltZQMxMTY2MTk5OTQxBHRwY0lkAzc0NDg=2D> in
this topic (4)
<http://groups=2Eyahoo=2Ecom/group/EnergyPlus_Support/post;_ylc=3DX3oDMTJwNXV0aGtt
BF9TAzk3MzU5NzE0BGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BG1zZ0lkAzc0OTgE
c2VjA2Z0cgRzbGsDcnBseQRzdGltZQMxMTY2MTk5OTQx?act=3Dreply&messageNum=3D7498>
Reply (via web post) | Start
<http://groups=2Eyahoo=2Ecom/group/EnergyPlus_Support/post;_ylc=3DX3oDMTJlaWlya3Vm
BF9TAzk3MzU5NzE0BGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwNmdHIEc2xr
A250cGMEc3RpbWUDMTE2NjE5OTk0MQ=2D=2D> a new topic
Messages
<http://groups=2Eyahoo=2Ecom/group/EnergyPlus_Support/messages;_ylc=3DX3oDMTJlZnI3
czhoBF9TAzk3MzU5NzE0BGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwNmdHIE
c2xrA21zZ3MEc3RpbWUDMTE2NjE5OTk0MQ=2D=2D> | Files
<http://groups=2Eyahoo=2Ecom/group/EnergyPlus_Support/files;_ylc=3DX3oDMTJmMXJqcmM
3BF9TAzk3MzU5NzE0BGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwNmdHIEc2x
rA2ZpbGVzBHN0aW1lAzExNjYxOTk5NDE=2D> | Photos
<http://groups=2Eyahoo=2Ecom/group/EnergyPlus_Support/photos;_ylc=3DX3oDMTJlMmZmMT
U0BF9TAzk3MzU5NzE0BGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwNmdHIEc2
xrA3Bob3QEc3RpbWUDMTE2NjE5OTk0MQ=2D=2D> | Members
<http://groups=2Eyahoo=2Ecom/group/EnergyPlus_Support/members;_ylc=3DX3oDMTJldTFlN
DI5BF9TAzk3MzU5NzE0BGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwNmdHIEc
2xrA21icnMEc3RpbWUDMTE2NjE5OTk0MQ=2D=2D> | Calendar
<http://groups=2Eyahoo=2Ecom/group/EnergyPlus_Support/calendar;_ylc=3DX3oDMTJkaTIx
NGprBF9TAzk3MzU5NzE0BGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwNmdHIE
c2xrA2NhbARzdGltZQMxMTY2MTk5OTQx>
The primary EnergyPlus web site is found at:
http://www=2Eenergyplus=2Egov
The group web site is:
http://groups=2Eyahoo=2Ecom/group/EnergyPlus_Support/
Attachments are not allowed =2D=2D please post any files to the appropriate
folder in the Files area of the Support Web Site=2E
EnergyPlus Documentation is searchable=2E Open EPlusMainMenu=2Eidf and press
the "search" button=2E
<http://groups=2Eyahoo=2Ecom/;_ylc=3DX3oDMTJkbXRibDRiBF9TAzk3MzU5NzE0BGdycElkAzMzO
Dc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwNmdHIEc2xrA2dmcARzdGltZQMxMTY2MTk5OTQx>
Yahoo! Groups
Change
<http://groups=2Eyahoo=2Ecom/group/EnergyPlus_Support/join;_ylc=3DX3oDMTJmbDZrZmxu
BF9TAzk3MzU5NzE0BGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwNmdHIEc2xr
A3N0bmdzBHN0aW1lAzExNjYxOTk5NDE=2D> settings via the Web (Yahoo! ID required)
Change settings via email: Switch
<mailto:EnergyPlus_Support=2Ddigest@yahoogroups=2Ecom?subject=3DEmail%20Delivery:%
20Digest> delivery to Daily Digest | Switch
<mailto:EnergyPlus_Support=2Dtraditional@yahoogroups=2Ecom?subject=3DChange%20Deli
very%20Format:%20Traditional> format to Traditional
Visit
<http://groups=2Eyahoo=2Ecom/group/EnergyPlus_Support;_ylc=3DX3oDMTJkM3V0YWtqBF9TA
zk3MzU5NzE0BGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwNmdHIEc2xrA2hwZ
gRzdGltZQMxMTY2MTk5OTQx> Your Group | Yahoo! Groups
<http://docs=2Eyahoo=2Ecom/info/terms/> Terms of Use | Unsubscribe
<mailto:EnergyPlus_Support=2Dunsubscribe@yahoogroups=2Ecom?subject=3D>
Recent Activity
* 4
New
<http://groups=2Eyahoo=2Ecom/group/EnergyPlus_Support/members;_ylc=3DX3oDMTJmOWo2M
XVlBF9TAzk3MzU5NzE0BGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwN2dGwEc
2xrA3ZtYnJzBHN0aW1lAzExNjYxOTk5NDE=2D> Members
* 11
New
<http://groups=2Eyahoo=2Ecom/group/EnergyPlus_Support/links;_ylc=3DX3oDMTJnZGQzNWs
1BF9TAzk3MzU5NzE0BGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwN2dGwEc2x
rA3ZsaW5rcwRzdGltZQMxMTY2MTk5OTQx> Links
* 3
New
<http://groups=2Eyahoo=2Ecom/group/EnergyPlus_Support/files;_ylc=3DX3oDMTJnbzlsZnQ
4BF9TAzk3MzU5NzE0BGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwN2dGwEc2x
rA3ZmaWxlcwRzdGltZQMxMTY2MTk5OTQx> Files
Visit
<http://groups=2Eyahoo=2Ecom/group/EnergyPlus_Support;_ylc=3DX3oDMTJlaGdldWV0BF9TA
zk3MzU5NzE0BGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwN2dGwEc2xrA3Zna
HAEc3RpbWUDMTE2NjE5OTk0MQ=2D=2D> Your Group
SPONSORED LINKS
* Backup
<http://groups=2Eyahoo=2Ecom/gads;_ylc=3DX3oDMTJjdXFtcDJzBF9TAzk3MzU5NzE0BF9wAzEEZ
3JwSWQDMzM4NzQ4OARncnBzcElkAzE3MDUwMDczODkEc2VjA3NsbW9kBHN0aW1lAzExNjYxOTk5N
DM=2D?t=3Dms&k=3DBackup+software+program&w1=3DBackup+software+program&w2=3DEmail+softw
are+program&w3=3DCad+software+program&w4=3DWedding+program+software&w5=3DMedical+s
oftware+program&c=3D5&s=3D143&g=3D2&=2Esig=3DmQ4Gv3Aim6Vq6h7KbSQKoQ> software program
* Email
<http://groups=2Eyahoo=2Ecom/gads;_ylc=3DX3oDMTJjam9mM2o3BF9TAzk3MzU5NzE0BF9wAzIEZ
3JwSWQDMzM4NzQ4OARncnBzcElkAzE3MDUwMDczODkEc2VjA3NsbW9kBHN0aW1lAzExNjYxOTk5N
DM=2D?t=3Dms&k=3DEmail+software+program&w1=3DBackup+software+program&w2=3DEmail+softwa
re+program&w3=3DCad+software+program&w4=3DWedding+program+software&w5=3DMedical+so
ftware+program&c=3D5&s=3D143&g=3D2&=2Esig=3DzbuhvU3GR=2DCNh3asafx1QQ> software program
* Cad
<http://groups=2Eyahoo=2Ecom/gads;_ylc=3DX3oDMTJjMTAxc3Y1BF9TAzk3MzU5NzE0BF9wAzMEZ
3JwSWQDMzM4NzQ4OARncnBzcElkAzE3MDUwMDczODkEc2VjA3NsbW9kBHN0aW1lAzExNjYxOTk5N
DM=2D?t=3Dms&k=3DCad+software+program&w1=3DBackup+software+program&w2=3DEmail+software
+program&w3=3DCad+software+program&w4=3DWedding+program+software&w5=3DMedical+soft
ware+program&c=3D5&s=3D143&g=3D2&=2Esig=3Di_rOWEWcncZW4RZwCR_lHQ> software program
* Wedding
<http://groups=2Eyahoo=2Ecom/gads;_ylc=3DX3oDMTJjM3NrMDYyBF9TAzk3MzU5NzE0BF9wAzQEZ
3JwSWQDMzM4NzQ4OARncnBzcElkAzE3MDUwMDczODkEc2VjA3NsbW9kBHN0aW1lAzExNjYxOTk5N
DM=2D?t=3Dms&k=3DWedding+program+software&w1=3DBackup+software+program&w2=3DEmail+soft
ware+program&w3=3DCad+software+program&w4=3DWedding+program+software&w5=3DMedical+
software+program&c=3D5&s=3D143&g=3D2&=2Esig=3D3m5jDL9wjLCcAWdRn6CuTg> program
software
* Medical
<http://groups=2Eyahoo=2Ecom/gads;_ylc=3DX3oDMTJjY3Y3bGtjBF9TAzk3MzU5NzE0BF9wAzUEZ
3JwSWQDMzM4NzQ4OARncnBzcElkAzE3MDUwMDczODkEc2VjA3NsbW9kBHN0aW1lAzExNjYxOTk5N
DM=2D?t=3Dms&k=3DMedical+software+program&w1=3DBackup+software+program&w2=3DEmail+soft
ware+program&w3=3DCad+software+program&w4=3DWedding+program+software&w5=3DMedical+
software+program&c=3D5&s=3D143&g=3D2&=2Esig=3D0IfA8Y1eOXL0SUDRR7NkeA> software
program
Yahoo! TV
<http://us=2Eard=2Eyahoo=2Ecom/SIG=3D12i6rk5rj/M=3D493064=2E9803235=2E10510228=2E8674578/D=3Dg
roups/S=3D1705007389:NC/Y=3DYAHOO/EXP=3D1166207143/A=3D3848429/R=3D0/SIG=3D10lh6opha/*ht
tp:/9=2Eyahoo=2Ecom/> "The 9"
Daily count down
of top Web finds=2E
Need traffic?
Drive
<http://us=2Eard=2Eyahoo=2Ecom/SIG=3D12i1lquk5/M=3D493064=2E9803227=2E10510220=2E8674578/D=3Dg
roups/S=3D1705007389:NC/Y=3DYAHOO/EXP=3D1166207143/A=3D3848644/R=3D0/SIG=3D131l83flq/*ht
tp:/searchmarketing=2Eyahoo=2Ecom/arp/srchv2=2Ephp?o=3DUS2006&cmp=3DYahoo&ctv=3DGroups5&
s=3DY&s2=3D&s3=3D&b=3D50> customers
With search ads
on Yahoo!
Sitebuilder
Over
<http://us=2Eard=2Eyahoo=2Ecom/SIG=3D12i4vdmk8/M=3D493064=2E9803229=2E10510223=2E8674578/D=3Dg
roups/S=3D1705007389:NC/Y=3DYAHOO/EXP=3D1166207143/A=3D4025308/R=3D0/SIG=3D12uhb64pb/*ht
tp:/us=2Erd=2Eyahoo=2Ecom/evt=3D44092/*http:/smallbusiness=2Eyahoo=2Ecom/webhosting/site
building=2Ephp> 380 Templates
Build and custo=2D
mize your web site
=2E
<http://geo=2Eyahoo=2Ecom/serv?s=3D97359714/grpId=3D3387488/grpspId=3D1705007389/msgId
=3D7498/stime=3D1166199941/nc1=3D3848429/nc2=3D3848644/nc3=3D4025308>
__,_=2E_,___
[Non-text portions of this message have been removed]
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/