Eric:

Yes, the two objects are very similar.  However, the ventilation object 
has more controls that can be applied (e.g., Minimum Indoor Temperature, 
Delta Temperature, Maximum Indoor Temperature, etc.) and considers the 
impacts of a fan (electric energy consumption AND fan heat added to the 
air stream .... see Field:Ventilation Type for the Ventilation object).

If your intake/exhaust fans are simply scheduled on or off based on time 
of day and you are willing to neglect the impacts of fan heat and fan 
electric consumption, then you can probably use the infiltration 
object.  If you want to model additional controls, then consider using 
the ventilation object.

Don

eric_zhou1223 wrote:

>Hi£¬
>
>I want to confirm one knowledge about ventilation and infiltration 
>object..
>If I do not care for the fan electric consumption, then I would think 
>these two objects in E+ are totally same. I checked the I/O 
>documentation and found they used the same equations. 
>Now I have an in-site test with a pair of intake/exaust fans. The 
>impact of the ventilation air on the load is only concern.
>Can I simply use the Infiltration Object to simulate it?
>
>Eric
>  
>



The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.idf and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/