Re: [EnergyPlus_Support] Fwd: Usage of chilled water return to supply another system
You might try creating an availability schedule from your weather file
that has 8760 entries. If outdoor WB > 57 schedule value = 1 else
schedule value = 0. Then apply this schedule as the availability
schedule for the equipment in the other HVAC system. Not sure if this
will work though.
miaoworld wrote:
> Has anyone had any suggestions on this?
>
> --- In EnergyPlus_Support@xxxxxxxxxxxxxxx
> <mailto:EnergyPlus_Support%40yahoogroups.com>, "miaoworld"
> <eric.yang@...> wrote:
>
> Greetings,
>
> I am not sure whether how to model this system correctly:
> The chiller is supplying 42 F chilled water with 54 F return. When
> outside air web bulb temperature is above 57 F, part of the return
> chilled water (54 F) is applied to another HVAC system as chilled
> water supply.
>
> When outside air web bulb temperature is below 57 F, the return
> chilled water goes back to the chiller.
>
> My initial thought is to build a separate case for the condition
> above 57F, which specifies the returned chilled water as an inlet for
> another HVAC system.
>
> Any suggestions would be greatly appreciated.
>
> Thanks.
>
> Eric (Miao)
>
> --- End forwarded message ---
>
>
--
Richard A. Raustad
Senior Research Engineer
Florida Solar Energy Center
University of Central Florida
1679 Clearlake Road
Cocoa, FL 32922-5703
Phone: (321) 638-1454
Fax: (321) 638-1439 or 1010
Visit our web site at: http://www.fsec.ucf.edu
UCF - From Promise to Prominence: Celebrating 40 Years
[Non-text portions of this message have been removed]
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/