Re: [EnergyPlus_Support] Fwd: Usage of chilled water return to supply another system
How many chilled water coils are there in the two HVAC systems? When WB<57 is
the second chilled water coil inactive?
If there is just one chilled water coil in each HVAC system, you could try the
following:
On the chilled water demand side inlet branch, put a pipe then a chilled water
coil in series. This chilled water coil serves the main HVAC system.
Then have a chilled water demand splitter with a chilled water coil and bypass
pipe in parallel. This chilled water coils serves the second HVAC system.
Use a schedule such as Rich described below to turn off the second chilled
water coil when WB<57. See SCHEDULE:FILE:COMMA.
I am not sure if this will really work - you may get errors.
If you need more chilled water coils in parallel (served directly by the
chiller), then I do not think that you will be able to model this with current
plant capabilities.
Mike
On 23 Jan 2007 at 11:31, Richard Raustad wrote:
> You might try creating an availability schedule from your weather file
> that has 8760 entries. If outdoor WB > 57 schedule value = 1 else
> schedule value = 0. Then apply this schedule as the availability
> schedule for the equipment in the other HVAC system. Not sure if this
> will work though.
>
> miaoworld wrote:
>
> > Has anyone had any suggestions on this?
> >
> > --- In EnergyPlus_Support@xxxxxxxxxxxxxxx
> > <mailto:EnergyPlus_Support%40yahoogroups.com>, "miaoworld"
> > <eric.yang@...> wrote:
> >
> > Greetings,
> >
> > I am not sure whether how to model this system correctly:
> > The chiller is supplying 42 F chilled water with 54 F return. When
> > outside air web bulb temperature is above 57 F, part of the return
> > chilled water (54 F) is applied to another HVAC system as chilled
> > water supply.
> >
> > When outside air web bulb temperature is below 57 F, the return
> > chilled water goes back to the chiller.
> >
> > My initial thought is to build a separate case for the condition
> > above 57F, which specifies the returned chilled water as an inlet for
> > another HVAC system.
> >
> > Any suggestions would be greatly appreciated.
> >
> > Thanks.
> >
> > Eric (Miao)
> >
> > --- End forwarded message ---
> >
> >
>
>
> --
> Richard A. Raustad
> Senior Research Engineer
> Florida Solar Energy Center
> University of Central Florida
> 1679 Clearlake Road
> Cocoa, FL 32922-5703
> Phone: (321) 638-1454
> Fax: (321) 638-1439 or 1010
> Visit our web site at: http://www.fsec.ucf.edu
>
> UCF - From Promise to Prominence: Celebrating 40 Years
>
>
>
> [Non-text portions of this message have been removed]
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
>
> EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the "search" button.
>
> Yahoo! Groups Links
>
>
>
>
>
========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/