Re: [EnergyPlus_Support] Dip in wall and roof outside temperature at 14:00 on 10/08
If it is a reasonably small input, send it to me. Also the weather file.
Make sure it is the exact input giving the symptom you describe.
Fred Buhl
wfbuhl@xxxxxxx
ooikoonbeng2004 wrote:
> Dear all,
>
> i ran a Task1.idf with MYS_Kuching_IWEC.epw and there is dip in the
> above temperatures to 26+ C from 30+ C before and after 14:00 for the
> wall and 50+ C on the roof before and after 14:00 for roof, only for
> the Oct 8th date of the typical design week.
>
> The above does not happen for the other days of the week.
> It also does not happen if i use Chicago weather file.
>
> Hope you can let me know the real reason (sun is directly above?) for
> this. i do not know how to upload files into this yahoo site.
>
> Loving kindness,
> ooi
>
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
>
> EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the "search" button.
>
> Yahoo! Groups Links
>
>
>
>
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/