Re: Res: [EnergyPlus_Support] Loads due to people



Also, remember that the "Number of People" field in the PEOPLE object also is 
used for autosizing outside air flow rates and is used by 
VENTILATION:MECHANICAL.  So remember not to use these features in these runs.

Mike


On 26 Jan 2007 at 0:47, Clarice Bleil de Souza wrote:

> Hi Fred,
> 
> Thank you for the reply. I've run 10 simulations from last night to today and it is possible to do it, yes. I did get the warning about having only 1W in the activity schedule. But I've checked the total people heat gains and the values are the same ones I've specified for number of people - which correspond to the total load due to people in the zone - so I assumed it worked!
> I'm not doing a comfort analysis so the results are meaningful.  
> 
> Thanks again for the reply
> 
> Regards,
> 
> Clarice
> 
> 
> ----- Mensagem original ----
> De: Fred Buhl <wfbuhl@xxxxxxx>
> Para: EnergyPlus_Support@xxxxxxxxxxxxxxx
> Enviadas: Quinta-feira, 25 de Janeiro de 2007 20:27:27
> Assunto: Re: [EnergyPlus_Support] Loads due to people
> 
> Clrice,
> 
> You can do this I think. The activity schedule values do not seem to be 
> altered in the code. You will get a warning
> message saying that the activity level is too low. And you will not be 
> able to use thermal comfort
> control, nor will you get any meaningful results from comfort 
> calculations. And you must input your
> own sensible fraction - do not let the program calculate it since it is 
> based on the activity level.
> 
> Fred
> 
> Clarice Bleil de Souza wrote:
> > Hi everybody,
> >
> > I want to run an EPlus simulation in which I set the amount of heat gains due to people directly. That is, instead of informing how many people I have in the zone and the activity schedule for it I would like to directly type the values in W for each zone - the same way the loads are specified in the lighting and equipment objects.
> >
> > Would it be correct to: 
> > - set the total load for each zone in W in the field number of people in the object people
> > - set a value of 1 for the activity schedule - all the time
> >
> > Would that be equivalent to assigning a value in W for each zone refering to the load due to occupancy? Seems to me I could do it that way after having a look at the input output reference guide but I'd like to confirm.
> >
> > It is said in the reference guide that the value assigned for activity schedule is modified based on a correlation to account for variations in temperture and that an internal algorithm is used to determine the latent and sensible fraction and that the radiant and convective portions are user specified. 
> >
> > If I specify in the people object the sensible fraction and the radiant fraction I would still have Eplus changing the value of the activity schedule based on the variations in temperature. Would those variations in temperature be depending on the value specified in the schedule only or depending on the product of the activity schedule value x the number of people in the zone? 
> >
> > If the changes due to variation in temperature are assigned to the product number of people X activity schedule value then it seems to me I could specify an activity schedule value of 1 and set the total load due to people for each zone directly in the number of people, correct?
> >
> > Please let me know about it
> >
> > Thank you in advance for this
> >
> > Regards,
> >
> > Clarice
> >
> > ____________ _________ _________ _________ _________ __
> > Fale com seus amigos de graça com o novo Yahoo! Messenger 
> > http://br.messenger .yahoo.com/ 
> >
> > [Non-text portions of this message have been removed]
> >
> >
> >
> > The primary EnergyPlus web site is found at:
> > http://www.energypl us.gov
> >
> > The group web site is:
> > http://groups. yahoo.com/ group/EnergyPlus _Support/
> >
> > Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
> >
> > EnergyPlus Documentation is searchable. Open EPlusMainMenu. idf and press the "search" button.
> > 
> > Yahoo! Groups Links
> >
> >
> >
> > 
> 
> 
> 
> __________________________________________________
> Fale com seus amigos  de graça com o novo Yahoo! Messenger 
> http://br.messenger.yahoo.com/ 
> 
> [Non-text portions of this message have been removed]
> 
> 
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
> 
> EnergyPlus Documentation is searchable.  Open EPlusMainMenu.idf and press the "search" button.
>  
> Yahoo! Groups Links
> 
> 
> 
> 
> 


========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support      
EnergyPlus-Support@xxxxxxxx





The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.idf and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/