Re: [EnergyPlus_Support] Airflow Network model doubt
David:
The document is correct. The AirflowNetwork model can calculate multizone
airflows driven by wind, either the HVAC system fan is off with inputs of
forced air distribution, or no forced air distribution system is specified.
In addition, the model can calculate multizone airflows driven by wind and
forced air through the forced air distribution system when the HVAC system
fan is on. In other words, the model calculates multizone airflows with wind
only or with wind and forced air together.
Natural ventilation is a way to deal with zoned airflows without including
air distribution system. The alternative way is to use the AirflowNetwork
model to calculate multizone airflows driven by wind with the similar
approach, excluding air distribution system.
EnergyPlus always calls Predictor and Corrector with and without HVAC
systems. The difference is that if there is no HVAC system, the system load
in the corrector is zero.
Lixing Gu
----- Original Message -----
From: "David Barrera" <davidabraham_b@xxxxxxxxx>
To: "Grupo EPlus" <energyplus_support@xxxxxxxxxxxxxxx>
Sent: Tuesday, February 06, 2007 3:58 PM
Subject: [EnergyPlus_Support] Airflow Network model doubt
> Dear all:
>
> In the documentation it is specified that
> AirflowNetwork model is able to calculate
> multizone airflows driven by wind when the HVAC system
> fan is off or when no forced air distribution system
> is specified for the simulation, is that correct? On
> the other hand I've read the Engineering Reference
> document for those topics related to advanced
> calculations of Natural Ventilation, (i.e.
> AirflowNetwork model considering no HVAC system
> defined), but all time it tells me about "simulate
> SYSTEM" or "predict SYSTEM capability", etc. Then how
> does the process of prediction-correction works if
> there's no "system to simulate"?
>
> Thanks a lot.
>
>
>
>
> ____________________________________________________________________________________
> It's here! Your new message!
> Get new email alerts with the free Yahoo! Toolbar.
> http://tools.search.yahoo.com/toolbar/features/mail/
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate
> folder in the Files area of the Support Web Site.
>
> EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press
> the "search" button.
>
> Yahoo! Groups Links
>
>
>
>
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/