RE: [EnergyPlus_Support] Solar Walls?
Eric,
In EnergyPlus, the brand name "Solar Wall" is referred to generically as
an unglazed transpired solar collector. I am not familiar with what
Design Builder will have provided you already, but your model will need
a full description of an HVAC air system with an outside air handler.
The transpired collector is connected to the Outdoor Air System by
listing it in an Air Loop Equipment List. It is positioned upstream of
the outdoor air mixer on the outdoor air intake path. Take a close look
at the example file that is provided with the release version of
EnergyPlus called "TranspiredCollectors.idf"
________________________________
From: EnergyPlus_Support@xxxxxxxxxxxxxxx
[mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of eric.mcmaster
Sent: Tuesday, February 13, 2007 3:15 PM
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Subject: [EnergyPlus_Support] Solar Walls?
Hello,
I am currently working on a project which involves
analyzing the effects of retrofit opportunities applied to commercial
office buildings.
One of the Retrofit opportunities I am attempting to model is a
Passive Solar wall. I have, up to now been using the assistance of the
third party Interface program "DesignBuilder" to aid me in the
development of my EnergyPlus Model and to this point I have been able
to produce a building with a Solar Wall that only contributes to the
natural ventilation of the building.
I am looking for assistance in using the Solar wall within the
mechanical ventilation system directly, to be used primarily as a
pre-heating system. What are the entry point that would need to be
altered
within the IDF file in order to define the necessary connections that
would make the air within the solar wall feed directly into the
HVAC system.
Any help you would be able give me would be greatly appreciated and if
you need further details on my modelling please let me know.
Thank You
Eric
[Non-text portions of this message have been removed]
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/