RE: [EnergyPlus_Support] program crashed after adding Induction unit
Thanks, Mike. The crash happened after I replace VAV reheat component
with FPIU components. The program didn't crash with VAV reheat
component. However, the results with VAV reheat component show that heat
exchanger condenser side flow rate is zero, but cooling tower flow rate
is not zero. I don't know whether it relates to this crash or not.
Thanks in advance.
Eric (Miao)
________________________________
From: EnergyPlus_Support@xxxxxxxxxxxxxxx
[mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of Michael J.
Witte
Sent: Monday, February 12, 2007 6:28 PM
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Subject: Re: [EnergyPlus_Support] program crashed after adding Induction
unit
I have reproduced the crash (after modifying the input to stay within
the
standard max/min limits in EnergyPlus). It is related to the plant
flows, but
I do not see the problem in the input. I will ask someone else for help.
Mike
On 12 Feb 2007 at 17:12, miaoworld wrote:
> Hi,
>
> I have tried to add an induction unit (FPIU) to the system and the
> program crashed without enough indication of the problem. I have
> tried to track where the problem, but no luck...
>
> The zone with FPIU is 119113 and the related components are listed at
> the end of the file (NF-EXP-CB.idf).
>
> For convenience, I also include them here at the end of this letter.
>
> Many thanks for your help. I really appreciate it.
>
> Eric (Miao)
>
>
>
> "NODE LIST,
> 119113 In Nodes, !- Node List Name
> 119113 in Node; !- Node_ID_1 Terminal unit air outlet,
> but inlet for zone
>
> NODE LIST,
> 119113 Exh Nodes, !- Node List Name
> 119113 ATU induc node; !- Node_ID_1
>
>
> SINGLE DUCT:CONST VOLUME:4 PIPE INDUC,
> 119113 FPIU, !- Name of unit
> COMPACT HVAC-ALWAYS 1, !- System availability schedule
> autosize, !- Maximum total air volume flow rate
> {m3/s}
> 2.0, !- Induction ratio
> 119113 Zone Equip Inlet, !- Terminal unit supply air inlet
> node
> 119113 ATU Induc Node, !- Terminal unit induced air inlet
> node
> 119113 In Node, !- Terminal unit air outlet node
> 119113 Reheat Coil HW Inlet, !- Hot water control node
> 119113 Cooling Coil CW Inlet,!- Cold water control node
> COIL:Water:SimpleHeating,!- Heating coil object
> 119113 Reheat Coil, !- Heating coil name
> autosize, !- Max hot water flow {m3/s}
> 0.00001, !- Min hot water flow {m3/s}
> 0.002, !- Heating Convergence Tolerance
> COIL:Water:Cooling, !- Cooling coil object
> 119113 Cooling Coil, !- Cooling coil name
> autosize, !- Max cold water flow {m3/s}
> 0.00001, !- Min cold water flow {m3/s}
> 0.002, !- Cooling Convergence Tolerance
> 119113 Zone Mixer; !- Zone mixer component name
>
> ZONE MIXER,
> 119113 Zone Mixer, !- Mixer Name
> 119113 Return Outlet, !- Zone Outlet_Node (outlet for ATU)
> 119113 Zone Equip Inlet,!- Inlet_Node_1
> 119113 Cooling coil air outlet; !- Inlet_Node_2 CW coil air
> outlet
>
> ZONE RETURN AIR PATH,
> 119113 Return Path, !- Return Air Path Name
> 119113 Return Outlet, !- Return Air Path Outlet Node
> ZONE MIXER, !- KEY--System Component Type 1
> 119113 Zone Mixer; !- Component Name 1
>
>
> !add by Eric
> COIL:Water:Cooling,
> 119113 Cooling Coil, !- Coil Name
> COMPACT HVAC-ALWAYS 1, !- Available Schedule
> autosize, !- Design Water Flow Rate of Coil {m3/s}
> autosize, !- Design Air Volume Flow Rate {m3/s}
> autosize, !- Design Inlet Water Temperature {C}
> autosize, !- Design Inlet Air Temperature {C}
> autosize, !- Design Outlet Air Temperature {C}
> autosize, !- Design Inlet Air Humidity Ratio {kg-
> H2O/kg-air}
> autosize, !- Design Outlet Air Humidity Ratio {kg-
> H2O/kg-air}
> 119113 Cooling Coil CW Inlet, !- Coil_Water_Inlet_Node
> 119113 Cooling Coil CW Outlet, !- Coil_Water_Outlet_Node
> 119113 Supply Inlet, !- Coil_Air_Inlet_Node
> 119113 Cooling coil air outlet, !- Coil_Air_Outlet_Node
> SimpleAnalysis, !- Type of Analysis
> CrossFlow; !- Heat Exchanger Configuration
>
>
> !Add by Eric
> BRANCH,
> 119113 Cooling Coil CW Branch, !- Branch Name
> , !- Maximum Branch Flow Rate {m3/s}
> COIL:Water:Cooling, !- Comp1 Type
> 119113 Cooling Coil, !- Comp1 Name
> 119113 Cooling Coil CW Inlet,!- Comp1 Inlet Node Name
> 119113 Cooling Coil CW Outlet, !- Comp1 Outlet Node Name
> ACTIVE; !- Comp1 Branch Control Type"
>
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov <http://www.energyplus.gov>
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
<http://groups.yahoo.com/group/EnergyPlus_Support/>
>
> Attachments are not allowed -- please post any files to the
appropriate folder in the Files area of the Support Web Site.
>
> EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and
press the "search" button.
>
> Yahoo! Groups Links
>
>
>
>
>
========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx <mailto:EnergyPlus-Support%40gard.com>
[Non-text portions of this message have been removed]
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/