Try manually sizing your boiler. The eio file shows the capacity and
flow rate as 0. There is a known issue with autosizing plant components
in certain cases.
Eric Yang wrote:
> Any suggestions on this question?
>
> ________________________________
>
> From: EnergyPlus_Support@xxxxxxxxxxxxxxx
> <mailto:EnergyPlus_Support%40yahoogroups.com>
> [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx
> <mailto:EnergyPlus_Support%40yahoogroups.com>] On Behalf Of Eric Yang
> Sent: Wednesday, February 14, 2007 11:26 AM
> To: EnergyPlus_Support@xxxxxxxxxxxxxxx
> <mailto:EnergyPlus_Support%40yahoogroups.com>
> Subject: [EnergyPlus_Support] Zero flow in HW pri-sec loop with Water
> Heater: Mixer
>
> Hi,
>
> I have experiencing zero flow for the primary heating water loop,
> though I have flow for the secondary heating water loop. The water
> heater is also having zero flows.
>
> I understand the water heater object is completely passive, but don't
> know how to solve the zero flow issues.
>
> Thanks in advance for your suggestions. I have uploaded the
> file "5ZoneVAV-Pri-SecLoop-hotwater-zeroflow.zip".
>
> Eric (Miao)
>
> [Non-text portions of this message have been removed]
>
>
--
Richard A. Raustad
Senior Research Engineer
Florida Solar Energy Center
University of Central Florida
1679 Clearlake Road
Cocoa, FL 32922-5703
Phone: (321) 638-1454
Fax: (321) 638-1439 or 1010
Visit our web site at: http://www.fsec.ucf.edu
UCF - From Promise to Prominence: Celebrating 40 Years
[Non-text portions of this message have been removed]
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/