[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

[EnergyPlus_Support] Re: Control schedules



ok. So i set the designdays to No and run the Kuching weather file 
and got a full years results. i sorted the WindAC outlet node temp 
in the .csv output file in descending/asceding order. 

Up to WindAC outlet node temp of 18 degrees C, its inlet temp is 
24.5 degrees C. The resistive zone temperature is below 25 degrees 
C. The coil of the WindAC is cooling the air and this seems fine. 

The next hour's WindowAC outlet temp is above 25 degrees C, its  
inlet temp is identical and the Resisitive zone temperature is +/-
0.3 degrees of the WindAC outlet node temp. This goes all the way to 
the max temp of 51.5 degress C for the 6mx6mx3m room. 

i shall try to make the room smaller or, if possible, increase the 
capacity of the cooling coil. 

best regards,
ooi

 
. The tempe, --- In EnergyPlus_Support@xxxxxxxxxxxxxxx, Linda Lawrie 
<linda@...> wrote:
>
> At 07:49 PM 2/23/2007, ooikoonbeng2004 wrote:
> >i ran the resulting .idf file with Kuching weather, but the
> >spreadsheet results show Chicago design days in the headings.
> 
> You will need to replace the Chicago design days in the input file 
> with appropriate ones for your location.  Your file ran the 
Chicago 
> design day weather specs with your Kuching location.
> 
> 
> Linda
> 
> EnergyPlus WebSite: http://www.energyplus.gov
> Owner: EnergyPlus_Support list
> Member: EnergyPlus Development Team
> 
> 
> 
> [Non-text portions of this message have been removed]
>




------------------------ Yahoo! Groups Sponsor --------------------~--> 
Check out the new improvements in Yahoo! Groups email.
http://us.click.yahoo.com/4It09A/fOaOAA/yQLSAA/dkFolB/TM
--------------------------------------------------------------------~-> 

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.idf and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/