1.  No.  There is no current auto import of CAD data.  One or more of the 
private-market user interface tools can display the CAD drawing and allow you 
to trace over it.  Shading devices are modeled 3 ways in EnergyPlus:  as a 
shade on the window surface, as a blind (movable slats) on the window surface, 
or as a collection of exterior shading surfaces (see SURFACE:SHADING:*).

2.  In EnergyPlus, a window (SURFACE:HEATTRANSFER:SUB, type=WINDOW) is required 
to transmit solar gains into the building.  Windows are also used as 
controllable openings for natural ventilation (see AIRFLOWNETWORK).  The solar 
transmittance of the window area does not change depending on the open or 
closed state of the window.  If the window is never glazed, simply an opening 
in the exterior wall, then define the glazing properties to be nearly perfect 
(e.g., transmittance = 0.99999, reflectances = 0.00001).

3.  EnergyPlus will determine the net direct and diffuse solar radiation which 
passes through the window, accounting for all shading devices.  If you specify, 
Solar Distribution=FullInteriorAndExterior or 
FullInteriorAndExteriorWithReflections) in the BUILDING object, EnergyPlus will 
determine which surfaces the incoming direct solar falls on and account for 
this in the heat balance for each surface.  The sunlit area and sunlit fraction 
can be reported for exterior surfaces, but not for interior surfaces.

4.  Yes, both inside and outside surface temperatures can be reported.

Mike


On 27 Feb 2007 at 22:59, neslihanturkmenoglu wrote:

> I am a very new user(I haven't used anything yet).Before, I sent a 
> message but I didn't get any answer. I hope someone hears me now:)
> 
> I want to simulate  cross ventilated zone having different types of 
> shading devices(19 types derived from 2 main- perpendicular to the 
> wall-parallel to the wall-alternatives) on exterior wall.I want to 
> see the effects of these devices to the cooling loads.
> 
> 1-I have modelled all these devices in CAD. So when I import my 
> drawings , will the program be able to recognise the information 
> about all these?
> 
> 2-When the window is open, how will I define a shading device?
> In the examples, there were glazed surfaces.
> 
> 3-As my window is open,ý want to consider the shaded and unshaded 
> areas caused by shading devices, emerge on floor. I have already 
> done this with other program. Will I import these informations to 
> energyplus or will I do all these through energyplus ?
> 
> 4-Can Energyplus calculate the surface temperatures?
> 
> 5-Can you advice me the easiest way to start?
> 
> thank you very much.
> 
> Neslihan T.BAYRAKTAR
> 
> 
> 
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
> 
> EnergyPlus Documentation is searchable.  Open EPlusMainMenu.idf and press the
> "search" button.
> 
> Yahoo! Groups Links
> 
> 
> 
> 
> 


========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support      
EnergyPlus-Support@xxxxxxxx





------------------------ Yahoo! Groups Sponsor --------------------~--> 
Great things are happening at Yahoo! Groups.  See the new email design.
http://us.click.yahoo.com/lOt0.A/hOaOAA/yQLSAA/dkFolB/TM
--------------------------------------------------------------------~-> 

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.idf and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/