Ooi:
The reason you got the error is that you don't have an object of Dual
Thermal Comfort Setpoint with Deadband:Fanger with object name = Test. After
definding the object, you may need two setpoint PMV schedules. The schedule
you mentioned looks like thermal comfort type schedule, which allows you to
change comfort type every time step.
Please look at an example file of FurnaceWithDXSystemComfortControl.idf,
which may give you a good starting point.
Best regards,
Lixing Gu
!- =========== ALL OBJECTS IN CLASS: DUAL THERMAL COMFORT SETPOINT WITH
DEADBAND:FANGER ===========
DUAL THERMAL COMFORT SETPOINT WITH DEADBAND:FANGER,
Test, !- Name
Heating PMV Setpoints, !- Fanger Thermal Comfort Heating Setpoint PMV
SCHEDULE Name
Cooling PMV Setpoints; !- Fanger Thermal Comfort Cooling Setpoint PMV
SCHEDULE Name
----- Original Message -----
From: "ooikoonbeng2004" <kooi@xxxxxxxxxxxxxxxx>
To: <EnergyPlus_Support@xxxxxxxxxxxxxxx>
Sent: Sunday, March 04, 2007 2:14 AM
Subject: [EnergyPlus_Support] Thermal Comfort and Thermostatic
>i am trying to control Thermal Comfort during office hours and switch
> to Thermostatic control during non-office hours as per Page 847 (pdf
> 855) of the IO documentation ver1.4.
>
> i got the following error:
> ** Severe ** GetZoneAirSetpoints: Could not find Dual Thermal Comfort
> Setpoint with Deadband Schedule:Fanger=TEST
>
> TEST is the name i gave to Thermal Comfort Control Type Name #1 in the
> Zone Control:Thermal Comfort object. Where do i enter the TEST?
> Setpoint Manager?
>
> i already have a Schedule type (PMV, range -4:4, Continuous Numeric)
> DaySchedule (Thermal Comfort Day, PMV, with hourly values of 4 and 0)
> WeekSchedule (Thermal Comfort Week, Thermal Comfort Day for all fields
> Schedule (Thermal Comfort, PMV, Thermal Comfort Week, 1/1 to 12/31)?
>
> Many Thanks,
> ooi
>
>
>
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate
> folder in the Files area of the Support Web Site.
>
> EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press
> the "search" button.
>
> Yahoo! Groups Links
>
>
>
>
------------------------ Yahoo! Groups Sponsor --------------------~-->
Yahoo! Groups gets a make over. See the new email design.
http://us.click.yahoo.com/hOt0.A/lOaOAA/yQLSAA/dkFolB/TM
--------------------------------------------------------------------~->
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/