Re: [EnergyPlus_Support] Re: What is the accurate component name?



Your error message indicates that you don't have a CHILLER:CONST COP 
of the name LITTLE CHILLER in your input file.

That object would look something like this:
   CHILLER:CONST COP,
     Little Chiller,          !- Chiller Name
     25000,                   !- Nominal Capacity {W}
     2.5,                     !- COP
     0.0011,                  !- Design Evaporator Volumetric Water 
Flow Rate {m3/s}
     0.0011,                  !- Design Condenser Volumetric Water 
Flow Rate {m3/s}
     Little Chiller Inlet Node,  !- Plant_Side_Inlet_Node
     Little Chiller Outlet Node,  !- Plant_Side_Outlet_Node
     Little Chiller Condenser Inlet Node,  !- Condenser_Side_Inlet_Node
     Little Chiller Condenser Outlet Node,  !- Condenser_Side_Outlet_Node
     Water Cooled,            !- Condenser Type
     VariableFlow;            !- Chiller Flow Mode

At the same time, you say  you took the DesiccantCVRhZoneRhCtrl input 
file but then you also say you changed it.

If you want a more accurate answer, please send or post your input file.


Linda

EnergyPlus WebSite: http://www.energyplus.gov
Owner: EnergyPlus_Support list
Member: EnergyPlus Development Team



[Non-text portions of this message have been removed]



------------------------ Yahoo! Groups Sponsor --------------------~--> 
Check out the new improvements in Yahoo! Groups email.
http://us.click.yahoo.com/4It09A/fOaOAA/yQLSAA/dkFolB/TM
--------------------------------------------------------------------~-> 

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.idf and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/