[EnergyPlus_Support] Re: What is the accurate component name?
--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, Linda Lawrie <linda@...>
wrote:
>Thank you!
I find th problem of this case. I missed one field that should be
filled you said.
Additionally, New problem has come.
In Zone Controls and Thermostat, I also enterend text in the field
as described in example file.
The result is below.
** Severe ** Single Heating Setpoint Schedule not found=HEATING
SETPOINTS
** ~~~ ** Reference SINGLE HEATING SETPOINT object=HEATING
SETPOINT WITH SB
** Severe ** Single Cooling Setpoint Schedule not found=COOLING
SETPOINTS
** ~~~ ** Reference SINGLE COOLING SETPOINT object=COOLING
SETPOINT WITH SB
** Severe ** Schedule=ZONE CONTROL TYPE SCHED
** ~~~ ** ..specifies control type 4 (Dual Set Point with
Deadband) as the control type. Not valid for this zone.
** ~~~ ** ..reference ZONE CONTROL:THERMOSTATIC=ZONE 152
THERMOSTAT
** ~~~ ** ..reference ZONE=152
** Severe ** Schedule=ZONE CONTROL TYPE SCHED
** ~~~ ** ..specifies control type 4 (Dual Set Point with
Deadband) as the control type. Not valid for this zone.
** ~~~ ** ..reference ZONE CONTROL:THERMOSTATIC=ZONE 50
THERMOSTAT
** ~~~ ** ..reference ZONE=50
** Severe ** Schedule=ZONE CONTROL TYPE SCHED
** ~~~ ** ..specifies control type 4 (Dual Set Point with
Deadband) as the control type. Not valid for this zone.
** ~~~ ** ..reference ZONE CONTROL:THERMOSTATIC=ZONE 82
THERMOSTAT
** ~~~ ** ..reference ZONE=82
I only entered the text that refered to example file and most have
similar name (except Zone name).
Sir Please tell me what is the problem.
> Your error message indicates that you don't have a CHILLER:CONST
COP
> of the name LITTLE CHILLER in your input file.
>
> That object would look something like this:
> CHILLER:CONST COP,
> Little Chiller, !- Chiller Name
> 25000, !- Nominal Capacity {W}
> 2.5, !- COP
> 0.0011, !- Design Evaporator Volumetric
Water
> Flow Rate {m3/s}
> 0.0011, !- Design Condenser Volumetric Water
> Flow Rate {m3/s}
> Little Chiller Inlet Node, !- Plant_Side_Inlet_Node
> Little Chiller Outlet Node, !- Plant_Side_Outlet_Node
> Little Chiller Condenser Inlet Node, !-
Condenser_Side_Inlet_Node
> Little Chiller Condenser Outlet Node, !-
Condenser_Side_Outlet_Node
> Water Cooled, !- Condenser Type
> VariableFlow; !- Chiller Flow Mode
>
> At the same time, you say you took the DesiccantCVRhZoneRhCtrl
input
> file but then you also say you changed it.
>
> If you want a more accurate answer, please send or post your input
file.
>
>
> Linda
>
> EnergyPlus WebSite: http://www.energyplus.gov
> Owner: EnergyPlus_Support list
> Member: EnergyPlus Development Team
>
>
>
> [Non-text portions of this message have been removed]
>
------------------------ Yahoo! Groups Sponsor --------------------~-->
Something is new at Yahoo! Groups. Check out the enhanced email design.
http://us.click.yahoo.com/kOt0.A/gOaOAA/yQLSAA/dkFolB/TM
--------------------------------------------------------------------~->
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/