Fred,
Thanks for the quick response. The reason I am having this issue is
because I am doing a parametric study in different climates. Does
this mean that for each climate I need to adjust the target hum
ratio in the system sizing?
I would really like to avoid doing this. Ideally, I just want to
make sure that I have 55F air downstream of the system fan and
frankly, I don't care too much about the humidity conditions.
However, the system sizing object forces me to keep going back and
adjusting the hum ratio to mitigate errors. How do other people do
this for parametric studies? Can I just set a SHR to avoid this?
Should the SHR be different for each climate?
--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, Fred Buhl <wfbuhl@...>
wrote:
>
> This is coming from the coil autosizing calculation. The coil
entering
> conditions
> are the mixed air conditions: recirc air (if any) mixed with
outside
> air. The outlet conditions
> are what you told the program in your System Siszing input as your
> desired design cooling
> supply air condiitons. So the message is saying that the entering
> moisture content is less
> than the leaving moisture content. Since a coil can't add
moisture, the
> choice is made to
> try to remove 1/2 of the entering moisture.
>
> Fred Buhl
>
> asheaffe wrote:
> > I am getting the following error on a coil:water:cooling
> >
> >
> >
> > ** Warning ** SizeWaterCoil: Coil="EXTERIOR ZONES COOLING
COIL",
> > Cooling Coil has leaving humidity ratio > entering humidity
ratio.
> > ** ~~~ ** ..will be sized for 50% of entering humidity
ratio.
> > ** Warning ** SizeWaterCoil: Coil="EXTERIOR ZONES COOLING
COIL",
> > Cooling Coil has part wet, part dry conditions.
> > ** ~~~ ** ..will be sized for 50% of design entering
humidity
> > ratio.
> > ** Warning ** SizeWaterCoil: Coil="OPERATING ZONE COOLING
COIL",
> > Cooling Coil has leaving humidity ratio > entering humidity
ratio.
> > ** ~~~ ** ..will be sized for 50% of entering humidity
ratio.
> > ** Warning ** SizeWaterCoil: Coil="OPERATING ZONE COOLING
COIL",
> > Cooling Coil has part wet, part dry conditions.
> > ** ~~~ ** ..will be sized for 50% of design entering
humidity
> > ratio.
> >
> >
> >
> > What does this error mean? In terms of the leaving humidity
ratio,
> > are we talking about the system design humidity ratio? This
error
> > is totally detroying the performance of the cooling coil.
> >
> > Thanks,
> >
> > Andrew
> >
> >
> >
> > The primary EnergyPlus web site is found at:
> > http://www.energyplus.gov
> >
> > The group web site is:
> > http://groups.yahoo.com/group/EnergyPlus_Support/
> >
> > Attachments are not allowed -- please post any files to the
appropriate folder in the Files area of the Support Web Site.
> >
> > EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf
and press the "search" button.
> >
> > Yahoo! Groups Links
> >
> >
> >
> >
>
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/