Re: [EnergyPlus_Support] Outside reveal shadowing
The outside reveal depth is defined by the coordinates of the window vertices
relative to the plane of the base wall surface. For example, if the corners of
a south-facing wall are at y=10, and window with a reveal of 0.2m would have
coordinates with y=10.2. This is discussed on p. 179 (pdf p.217) of the Input
Output Reference.
The inside reveal must be defined using the window frame and divider inputs.
Note that the material thicknesses are not known by the solar shading
algorithms. Please send me the input file which causes a crash, so we can add
a trap with an error message.
Mike
On 22 Mar 2007 at 12:29, Renato Sousa wrote:
> Dear EnergyPlus users,
>
> I want to see the effect in solar gains of placing a window in the outer or in
> the inner surface of a wall with 0.45 m thickness. From what I've seen in the
> engineering reference, this is related with the outside reveal depth (ORD),
> which is calculated from the inside reveal depth (IRD) that we input and from
> the wall thickness (WT) and glazing thickness (GT). As far as I understood, ORD
> = WT - IRD - GT, since ORD and IRD are measured from the outside and inside
> glazing surfaces until the respective wall surfaces.
>
> So for changing the glazing position between the inner and outer wall
> surfaces we should change the IRD value. The problem is that changing this
> value from its default (0), EnergyPlus crashes.
> Isn't by default EnergyPlus considering the glazing in the outer surface? (I
> think is not consistent with IRD=0 by default...)
>
> Did anyone try to analyse a similar problem? Is there anything else that
> should be changed?
>
> Thank you in advance.
>
>
> Renato Sousa
>
> Tel: +351 919 316 221 | E-mail: renato.sousa@xxxxxxxxxxxxx
>
>
>
> ___________________________________________________
>
> FluidInova, Engenharia de Fluidos, SA
>
> TECMAIA - Parque de Ciência e Tecnologia da Maia
>
> Rua Engº Frederico Ulrich, nº 2650 | 4470-605 Moreira da Maia | Portugal
>
>
> Tel: +351 229 408 265 | Fax: +351 229 408 266
>
> E-mail: <mailto:geral@xxxxxxxxxxxxx> geral@xxxxxxxxxxxxx | Web:
> www.fluidinova.pt/
>
>
>
>
>
>
> [Non-text portions of this message have been removed]
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
>
> EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the
> "search" button.
>
> Yahoo! Groups Links
>
>
>
>
>
========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/