As Don and Rich have explained, the HVAC system timestep does vary, and you can
report results at the timestep level, but this is not relevant to what you are
trying to model. Each HVAC timestep in EnergyPlus is a quasi-steady-state
simulation. For the gas heating coil cycling loss is modeled by looking at the
quasi-steady part load ratio and making an adjustment to the efficiency through
the "Part load fraction correlation (function of part load ratio)" curve in
COIL:Gas:Heating.
For example, if the load on the furnace from 9:00am to 9:30 am is 50% of
capacity, it doesn't matter if EnergyPlus simulates two 15-minute HVAC
timesteps, or 30 1-minute HVAC timesteps. Each timestep will evaluate the
efficiency at 50% part-load. There may be minor differences in results when
the timestep shifts down, but you should not need to be concerned with the
length of timestep. But, you do need to make sure the Part load fraction
correlation curve accurately represents the type of equipment you are studying.
Mike
On 4 Apr 2007 at 10:30, taharvey2001 wrote:
> I'd like to be able to model a standard constant volume residential
> forced air heater in EnergyPlus and see the impact of Sizing on
> efficiency and heater cycling.
>
> I haven't been able to figure out how to model the heater
> appropriately in E+ or and make sure the heater has sufficiently small
> timestep resolution so the heater can cycle, and the difference in
> efficiency can be seen.
>
> As I understand, the HVAC system timestep is decoupled from the 15
> minute building timestep, allowing it to free-run with an adaptive
> timestep (down to seconds if need be) - is this true, and is there
> anything that need to be done to enable this behavior? Is there anyway
> to see the high-res HVAC transients in the output?
>
> What is the best way to get a const. volume, const BTU heater to model
> residential forced air systems?
>
> thanks,
>
> troy
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
>
> EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the
> Documentation link and press the "search" button.
>
> Yahoo! Groups Links
>
>
>
>
>
========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/