Re: [EnergyPlus_Support] Residential heater sizing and cycling question



If you output the report variables using a "detailed" frequency, you 
will see when the HVAC system time steps are reduced. Typically this 
happens when there is a change in zone temperature. If your simulation 
maintains a constant indoor temperature, you may not see this behavior. 
If your thermostat schedule uses a setback strategy (e.g. 20C during the 
day and 18C during the night) you will most likely see the HVAC system 
time step shorten when the thermostat temperature changes.

taharvey2001 wrote:

> I'd like to be able to model a standard constant volume residential
> forced air heater in EnergyPlus and see the impact of Sizing on
> efficiency and heater cycling.
>
> I haven't been able to figure out how to model the heater
> appropriately in E+ or and make sure the heater has sufficiently small
> timestep resolution so the heater can cycle, and the difference in
> efficiency can be seen.
>
> As I understand, the HVAC system timestep is decoupled from the 15
> minute building timestep, allowing it to free-run with an adaptive
> timestep (down to seconds if need be) - is this true, and is there
> anything that need to be done to enable this behavior? Is there anyway
> to see the high-res HVAC transients in the output?
>
> What is the best way to get a const. volume, const BTU heater to model
> residential forced air systems?
>
> thanks,
>
> troy
>
>  


-- 
Richard A. Raustad
Senior Research Engineer
Florida Solar Energy Center
University of Central Florida
1679 Clearlake Road
Cocoa, FL  32922-5703
Phone:   (321) 638-1454
Fax:     (321) 638-1439 or 1010
Visit our web site at: http://www.fsec.ucf.edu

UCF - From Promise to Prominence: Celebrating 40 Years



[Non-text portions of this message have been removed]



The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/