Re: [EnergyPlus_Support] Re: A question about Supply Fan.



You can use REPORT:TABLE:MONTHLY to do this.  

Report:Table:Monthly,
Air Loop Fan Power Consumption, !- Name
, !- DigitsAfterDecimal
Air Loop Total Heating Coil Energy, HoursPositive,
Air Loop Fan Electric Consumption, SumOrAverageDuringHoursShown,
Air Loop Total Heating Coil Energy, HoursNonPositive,
Air Loop Fan Electric Consumption, SumOrAverageDuringHoursShown,
Air Loop Fan Electric Consumption, SumOrAverage;

The first two fields will report the fan energy when the heating coil is 
active.  The next two will report the fan energy when the heating coil is not 
active, implying cooling operation.  The last field is a check; it should equal 
the sum of columns 2 and 4.

Mike


On 11 Apr 2007 at 15:37, xjtu.guowei wrote:

> Thank you very much for your reply.
> 
> But sometimes during the period of time step, both the heating and
> cooling are greater than zero. So it is hard to use spreadsheet to sum
>   heating and cooling separately.
> 
> And if we use the detailed reports, the data file will be very large,
> EXCEL cannot load completely.
> 
> Would you like to give some help about that? Thank you very much.
> 
> Wei
> 
> --- In EnergyPlus_Support@xxxxxxxxxxxxxxx, Richard Raustad
> <RRaustad@...> wrote:
> >
> > If you want to know how much fan energy is consumed in cooling mode and 
> > how much fan energy is consumed in heating mode, then you will have to 
> > use a spreadsheet to perform the calculations. Report the fan, cooling 
> > and heating energy. Then in the spreadsheet, sum the fan energy when 
> > cooling energy is greater than 0. Do the same for the fan when heating 
> > energy is greater than 0.
> > 
> > Richard Raustad wrote:
> > 
> > > Use the Fan Electric Power and Fan Electric Consumption report
> > > variables. These variables are described in the InputOutputReference
> > > document for the Fan:Simple:OnOff object.
> > >
> > > xjtu.guowei wrote:
> > >
> > > > Dear All:
> > > >
> > > > I am doing a building simulation in which the compact HVAC is used.
> > > > There is a field which is supply fan operation mode. I have
> chosen the
> > > > cycling in stead of continuous. You know the fan will be working
> when
> > > > either cooling or heating needs to be supplied to the zone.
> > > >
> > > > I would like to know how much of the power consumed by the
> supply fan
> > > > is combining with the cooling or heating separately not totally.
> > > >
> > > > Thank you very much.
> > > >
> > > > wei
> > > >
> > > >
> > >
> > > -- 
> > > Richard A. Raustad
> > > Senior Research Engineer
> > > Florida Solar Energy Center
> > > University of Central Florida
> > > 1679 Clearlake Road
> > > Cocoa, FL 32922-5703
> > > Phone: (321) 638-1454
> > > Fax: (321) 638-1439 or 1010
> > > Visit our web site at: http://www.fsec.ucf.edu
> <http://www.fsec.ucf.edu>
> > >
> > > UCF - From Promise to Prominence: Celebrating 40 Years
> > >
> > > [Non-text portions of this message have been removed]
> > >
> > >  
> > 
> > 
> > -- 
> > Richard A. Raustad
> > Senior Research Engineer
> > Florida Solar Energy Center
> > University of Central Florida
> > 1679 Clearlake Road
> > Cocoa, FL  32922-5703
> > Phone:   (321) 638-1454
> > Fax:     (321) 638-1439 or 1010
> > Visit our web site at: http://www.fsec.ucf.edu
> > 
> > UCF - From Promise to Prominence: Celebrating 40 Years
> > 
> > 
> > 
> > [Non-text portions of this message have been removed]
> >
> 
> 
> 
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
> 
> EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the
> Documentation link and press the "search" button.
> 
> Yahoo! Groups Links
> 
> 
> 
> 
> 


========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support      
EnergyPlus-Support@xxxxxxxx





The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/