[EnergyPlus_Support] Re: Window AC or Unitary - Coil:DX:CoolingBypassFactorEmpirical



Thanks Linda for the quick response. 

 

>From the .eio file, I can get

 

Component Sizing, AIR CONDITIONER:WINDOW:CYCLING, ZONE1WINDAC, maximum air
flow rate [m3/s],   1.3545    

Component Sizing, AIR CONDITIONER:WINDOW:CYCLING, ZONE1WINDAC, maximum
outside air flow rate [m3/s],  0.28320E-01

Component Sizing, FAN:SIMPLE:ONOFF, ZONE1WINDACFAN, Max Flow Rate [m3/s],
1.3545    

Component Sizing, COIL:DX:COOLINGBYPASSFACTOREMPIRICAL, ZONE1WINDACDXCOIL,
Rated Air Volume Flow Rate [m3/s],   1.3545    

Component Sizing, COIL:DX:COOLINGBYPASSFACTOREMPIRICAL, ZONE1WINDACDXCOIL,
Rated Total Cooling Capacity (gross) [W],   22907.    

Component Sizing, COIL:DX:COOLINGBYPASSFACTOREMPIRICAL, ZONE1WINDACDXCOIL,
Rated SHR,  0.64721    

Environment:WarmupDays,  3

 

Off-hand, the 22907W, or 23KW is high compared to the total 7KW that has
been used in this room/zone for some years. 

 

I shall use the WarmupDays of 3 to plan for the next time when I have to
validate the HVAC part, after I validate the Building envelope. 

 

Kind regards

ooi  



[Non-text portions of this message have been removed]



The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/