If you have split your surface into 2 different constructions (and 
surfaces), then you will have to also split your door into 2 surfaces 
(with the same construction). Each surface of the split door should lie 
within the vertices of the corresponding surface it is attached to.

ooikoonbeng2004 wrote:

> There is a door across the top and bottom of a wall. Top and bottom
> has different constructions and have been specified with 4 vertices
> each. The following is the err file:
>
> Program Version,EnergyPlus 1.4.0.025, 4/14/2007 11:29 AM,IDD_Version
> 1.4.0.025
> ************* Beginning Zone Sizing Calculations
> ** Warning ** Calculated design heating load for zone=RESISTIVE
> ZONE is zero.
> ** ~~~ ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC
> inputs.
> ************* Testing Individual Branch Integrity
> ************* All Branches passed integrity testing
> ************* Testing Individual Supply Air Path Integrity
> ************* All Supply Air Paths passed integrity testing
> ************* Testing Individual Return Air Path Integrity
> ************* All Return Air Paths passed integrity testing
> ************* No node connection errors were found.
> *************
> ************* ===== Recurring Surface Error Summary =====
> ************* The following surface error messages occurred.
> *************
> ************* Base Surface does not surround subsurface errors
> occuring...
> ************* Check that the SurfaceGeometry object is expressing
> the proper starting corner and direction [CounterClockwise/Clockwise]
> *************
> ** Warning ** Base surface does not surround subsurface (CHKSBS),
> Overlap Status=Partial-Overlap
> ** ~~~ ** The base surround errors occurred 1 times.
> ** ~~~ ** Surface "ZN001:WALL001TOP" overlaps
> SubSurface "WALL 1:DOOR"
> *************
> ** ~~~ ** The base surround errors occurred 1 times (total).
> *************
> ************* EnergyPlus Completed Successfully-- 2 Warning; 0
> Severe Errors; Elapsed Time=00hr 00min 12.00sec
>
> Is it easy to tell the reason? if not i shall read more the
> documentation to find out. Many thanks. ooi
>
>  


-- 
Richard A. Raustad
Senior Research Engineer
Florida Solar Energy Center
University of Central Florida
1679 Clearlake Road
Cocoa, FL  32922-5703
Phone:   (321) 638-1454
Fax:     (321) 638-1439 or 1010
Visit our web site at: http://www.fsec.ucf.edu

UCF - From Promise to Prominence: Celebrating 40 Years



[Non-text portions of this message have been removed]



The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/