[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]
Re: [EnergyPlus_Support] zero air loop mass flow rate
Hello Mike,
thanks a lot for your help. I chanced all air flow rates to the same
value. But I get only an air flow, if I set a minimal air flow rate for
the fan. Why doesn't variate the air flow to meet the zone load? I'm
sorry, if this is a basic question.
thanks in advance
sebastian
Michael J. Witte schrieb:
> In the BRANCH object "Branch_Air_supply_in", the maximum flow rate is set to
> zero. (Version 2.0 does generate a warning message for this condition - one of
> many reasons to upgrade!)
>
> Program Version,EnergyPlus 2.0.0.025, 4/13/2007 9:29 AM,IDD_Version 2.0.0.025
> ** Severe ** Branch=BRANCH_AIR_SUPPLY_IN is an air branch with zero max
> flow rate.
>
>
> When specifying hard values for sizes (instead of autosize), the maximum (or
> design) flow rate in the AIR PRIMARY LOOP, BRANCH, FAN, and other components on
> the air loop main branch must all have the same value. And the sum of the
> terminal unit design flow rates must equal the main air loop flow rate.
>
> Mike
>
>
> On 13 Apr 2007 at 15:58, Sebastian Dietz wrote:
>
>
>> Hello erverybody,
>>
>> I'm simulating one zone modell to get familíar with Energy Plus.
>> Therefor I constructed an simple Air Loop. The primary air system side
>> contains Fan and coil:water:simple:heating elements, the zone equipment
>> side contains a singleduct:vav:noreheat element. I compared my file
>> serveral times with example files, but I have still no mass flow rate in
>> the Air Loop. I don't get any warnings, thus it seems to be a set point
>> or controller fault. Does anybody have an idea, how to solve the problem?
>> I added my simpleairloop.idf file to the web
>>
>> Thanks in davance
>> sebastian
>>
>> --
>> Sebastian Dietz
>> Fraunhofer-Institut for Solare Energiesysteme ISE
>> Heidenhofstrasse 2, 79110 Freiburg, Germany
>> Phone: +49 (0) 7 61/ 45 88-51 36
>> Sebastian.Dietz@xxxxxxxxxxxxxxxxx
>> http://www.ise.fraunhofer.de
>> -------------------------------------------
>>
>>
>>
>> The primary EnergyPlus web site is found at:
>> http://www.energyplus.gov
>>
>> The group web site is:
>> http://groups.yahoo.com/group/EnergyPlus_Support/
>>
>> Attachments are not allowed -- please post any files to the appropriate folder
>> in the Files area of the Support Web Site.
>>
>> EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the
>> Documentation link and press the "search" button.
>>
>> Yahoo! Groups Links
>>
>>
>>
>>
>>
>>
>
>
> ========================================================
> Michael J. Witte, GARD Analytics, Inc.
> EnergyPlus Testing and Support
> EnergyPlus-Support@xxxxxxxx
>
>
>
>
>
--
Sebastian Dietz
Fraunhofer-Institut for Solare Energiesysteme ISE
Heidenhofstrasse 2, 79110 Freiburg, Germany
Phone: +49 (0) 7 61/ 45 88-51 36
Sebastian.Dietz@xxxxxxxxxxxxxxxxx
http://www.ise.fraunhofer.de
-------------------------------------------
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/