Re: [EnergyPlus_Support] zero air loop mass flow rate
The thermostat is a heating-only thermostat, so it will not open the VAV damper
for cooling. Also SINGLE DUCT:VAV:NOREHEAT is a cooling-only VAV terminal
unit, so it will not respond to a heating request from the thermostat. If you
want the system to vary airflow rate to meet heating loads, then use SINGLE
DUCT:VAVHEATANDCOOL:NOREHEAT.
Mike
On 16 Apr 2007 at 16:26, Sebastian Dietz wrote:
> Hello Mike,
>
> thanks a lot for your help. I chanced all air flow rates to the same
> value. But I get only an air flow, if I set a minimal air flow rate for
> the fan. Why doesn't variate the air flow to meet the zone load? I'm
> sorry, if this is a basic question.
>
> thanks in advance
> sebastian
>
========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/