Re: [EnergyPlus_Support] warnings about "temperatuer out of range"
Thank you Mike. I changed to Coil:water:Cooling and these warning are gone.
However, when I change some of the zoning arrangement. I got another type of warings
** SolveAirLoopControllers: Maximum iterations (50) exceeded for VAV SYS 4, at SHENZHEN - CHN TMY3-594930 WMO#=594930, 07/07 08:00 - 08:02
Could you please or other experienced fellow tell what issues cause these warings and what can be done to solve this problem?
Thank you very much in advance.
Regards,
David
"Michael J. Witte" <mjwitte@xxxxxxxx> wrote:
These types of errors almost always come from initial iterations in the
detailed cooling coil model which result in calling a Pyschrometric function
with an impossible humidity condition. There is not actually a temperature of
35286.37 occuring within the simulation.
Currently Compact HVAC uses COIL:Water:DetailedFlatCooling to model chilled
water coils. For certain types of applications, this model generates such
warnings. Since these warnings usually result during early iterations within
the coil model, they typically do not impact the results, but I cannot say that
with certainty for all cases.
To eliminate these warnings, try editing the expidf file (saved under a new
name.idf) and replace the COIL:Water:DetailedFlatCooling objects (and all
occurences of COIL:Water:DetailedFlatCooling) with COIL:Water:Cooling. Future
versions of Compact HVAC will allow the user to select the specific chilled
water coil model to be used.
Mike
On 12 Apr 2007 at 18:48, Zhen Tian wrote:
> Dear all,
>
> I am simulating base case design for an office building located in ShenZhen
> (ASHRAE Zone 2A) and experiened the following warnings:
>
> The system is VAV reheat and all system components are autosized and generated
> with Compact HVAC object.
>
> Could someone tell me that whether these warnings will affect my simulation
> results? What inputs cause these warnings and how can I fix these warnings?
>
> Thank you very much in advance.
>
> Regards,
>
> David
>
> ** Warning ** Temperature out of range [-100. to 200.] (PsyPsatFnTemp)
> ** ~~~ ** Occurrence info=SHENZHEN - CHN TMY3-594930 WMO#=594930, 01/02
> 00:45 - 01:00 ** ~~~ ** Input Temperature=35286.37 ** Warning **
> Temperature out of range [-100. to 200.] (PsyPsatFnTemp) ** ~~~ **
> Occurrence info=SHENZHEN - CHN TMY3-594930 WMO#=594930, 01/02 01:00 - 01:15
> ** ~~~ ** Input Temperature=102750.91
> ........
>
>
>
>
> ---------------------------------
> Expecting? Get great news right away with email Auto-Check.
> Try the Yahoo! Mail Beta.
>
> [Non-text portions of this message have been removed]
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
>
> EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the
> Documentation link and press the "search" button.
>
> Yahoo! Groups Links
>
>
>
>
>
========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
---------------------------------
Ahhh...imagining that irresistible "new car" smell?
Check outnew cars at Yahoo! Autos.
[Non-text portions of this message have been removed]
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/