>From the error message, you know that the problem lies with "VAV SYS 4".  Check 
for misconnections, bad controls (incorrect set point or control nodes), 
undersized capacities, or battling coils.

Mike


On 17 Apr 2007 at 2:57, Zhen Tian wrote:

> Thank you Mike. I changed to Coil:water:Cooling and these warning are gone.
>   However, when I change some of the zoning arrangement. I got another type of
>   warings ** SolveAirLoopControllers: Maximum iterations (50) exceeded for VAV
>   SYS 4, at SHENZHEN - CHN TMY3-594930 WMO#=594930, 07/07 08:00 - 08:02
> 
>   Could you please or other experienced fellow  tell what issues cause these
>   warings and what can be done to solve this problem?
> 
>   Thank you very much in advance.
> 
>   Regards,
> 
>   David
> 
> 
> "Michael J. Witte" <mjwitte@xxxxxxxx> wrote:
>           These types of errors almost always come from initial iterations in
>           the 
> detailed cooling coil model which result in calling a Pyschrometric function
> with an impossible humidity condition. There is not actually a temperature of
> 35286.37 occuring within the simulation. 
> 
> Currently Compact HVAC uses COIL:Water:DetailedFlatCooling to model chilled
> water coils. For certain types of applications, this model generates such
> warnings. Since these warnings usually result during early iterations within the
> coil model, they typically do not impact the results, but I cannot say that with
> certainty for all cases. 
> 
> To eliminate these warnings, try editing the expidf file (saved under a new
> name.idf) and replace the COIL:Water:DetailedFlatCooling objects (and all
> occurences of COIL:Water:DetailedFlatCooling) with COIL:Water:Cooling. Future
> versions of Compact HVAC will allow the user to select the specific chilled
> water coil model to be used.
> 
> Mike
> 
> On 12 Apr 2007 at 18:48, Zhen Tian wrote:
> 
> > Dear all,
> > 
> > I am simulating base case design for an office building located in ShenZhen
> > (ASHRAE Zone 2A) and experiened the following warnings:
> > 
> > The system is VAV reheat and all system components are autosized and generated
> > with Compact HVAC object. 
> > 
> > Could someone tell me that whether these warnings will affect my simulation
> > results? What inputs cause these warnings and how can I fix these warnings?
> > 
> > Thank you very much in advance.
> > 
> > Regards,
> > 
> > David
> > 
> > ** Warning ** Temperature out of range [-100. to 200.] (PsyPsatFnTemp)
> > ** ~~~ ** Occurrence info=SHENZHEN - CHN TMY3-594930 WMO#=594930, 01/02
> > 00:45 - 01:00 ** ~~~ ** Input Temperature=35286.37 ** Warning **
> > Temperature out of range [-100. to 200.] (PsyPsatFnTemp) ** ~~~ ** 
> > Occurrence info=SHENZHEN - CHN TMY3-594930 WMO#=594930, 01/02 01:00 - 01:15 **
> > ~~~ ** Input Temperature=102750.91 ........
> > 
> > 
> > 
> > 
> > ---------------------------------
> > Expecting? Get great news right away with email Auto-Check.
> > Try the Yahoo! Mail Beta.
> > 
> > [Non-text portions of this message have been removed]
> > 
> > 
> > 
> > The primary EnergyPlus web site is found at:
> > http://www.energyplus.gov
> > 
> > The group web site is:
> > http://groups.yahoo.com/group/EnergyPlus_Support/
> > 
> > Attachments are not allowed -- please post any files to the appropriate folder
> > in the Files area of the Support Web Site.
> > 
> > EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the
> > Documentation link and press the "search" button.
> > 
> > Yahoo! Groups Links
> > 
> > 
> > 
> > 
> > 
> 
> ========================================================
> Michael J. Witte, GARD Analytics, Inc.
> EnergyPlus Testing and Support 
> EnergyPlus-Support@xxxxxxxx
> 
> 
> 
> 
> 
> 
> ---------------------------------
> Ahhh...imagining that irresistible "new car" smell?
>  Check outnew cars at Yahoo! Autos.
> 
> [Non-text portions of this message have been removed]
> 
> 
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
> 
> EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the
> Documentation link and press the "search" button.
> 
> Yahoo! Groups Links
> 
> 
> 
> 
> 


========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support      
EnergyPlus-Support@xxxxxxxx





The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/