> Unfortunately, there is no good solution to modeling this case.  
Here is a 
> (long) answer laying out some of the issues.
> 
> Mike
> 
> It is extremely difficult to model the interactions between 
thermal zones which 
> are connected by a large opening.  If the zones are controlled to 
the same 
> conditions, then there is little to be gained by making them 
interact, so you 
> could neglect any connections between the zones.  In fact, if this 
is the case, 
> you might consider combining the spaces into a single thermal 
zone. If you 
> expect the zones to have significantly different temperatures 
and/or 
> humidities, then use one of the following options.  If they are 
modeled as 
> separate zones, EnergyPlus models only what is explicitly 
described in the 
> input file, so simply leaving a void (no surfaces) between two 
zones will 
> accomplish nothing - the two zones will not be connected.  The 
main 
> interactions which occur across the dividing line between two 
zones which are 
> fully open to each other are:
> 
> 1.  Convection or airflow, which will transfer both sensible heat 
and moisture. 
>  Some modelers use MIXING (one-way flow) or CROSS MIXING (two-way 
flow) to move 
> air between the zones, but the user must specify airflow rates and 
schedules 
> for this flow, and it cannot be automatically linked to HVAC 
system operation.  
> Other modelers use AirFlowNetwork with large vertical openings 
between the 
> zones as well as other openings and cracks in the exterior 
envelope to provide 
> the driving forces.  It can also be connected with the HVAC system 
(for limited 
> system types).  This requires a much higher level of detailed 
input and should 
> be used only if the detailed specification data is available.  If 
the two zones 
> are controlled to similar conditions, this effect could be safely 
neglected.
> 
> 2.  Solar gains and daylighting.  The only way to pass solar and 
daylight from 
> one zone to the next is through a window or glass door  described 
as a 
> subsurface (Surface:HeatTransfer:Sub) on an interzone wall 
surface.  Note that 
> all solar is diffuse after passing through an interior window.  
> 
> 3. Radiant (long-wave thermal) transfer.  There is currently no 
direct radiant 
> exchange between surfaces in different thermal zones.  Windows in 
EnergyPlus 
> are opaque to direct radiant exchange, so an interzone window will 
not behave 
> any differently than an opaque interzone surface for this aspect. 
However, a 
> large interzone surface (opaque or window) would result in some 
indirect 
> radiant exchange since the interzone surface will exchange 
directly with 
> surfaces in zone A and in zone B.  The surface thermal resistance 
should be low 
> in order to most closely approximate this effect.
> 
> 4. Conduction.  If an interzone surface is place between the two 
zones, it will 
> conduct sensible heat between the two zones.  Using a low thermal 
resistance 
> helps to move radiant exchange between the zones.
> 
> 5. Visible and thermal radiant output from internal gains.  These 
gains will 
> not cross zone boundaries.  But again, they will impact any 
interzone surfaces, 
> so some of the energy may move across to the next zone.
> 
> 
> 
> On 17 Apr 2007 at 7:04, benteqman wrote:
> 
> > Hi all,
> > I am hoping this will be straight forward to answer. How do you 
model 
> > to zones which do not have a wall between them?  Should I leave 
the 
> > imaginary surface out, or should I define it by a wall with a 
full size 
> > window with miniscual heat transfer properties?
> > 
> > If there is signicant daylighting, defining the imaginary 
surface a 
> > wall would block this out..
> > I look forward to a response.
> > Regards
> > Ben
> > 
> > 
> > 
> > The primary EnergyPlus web site is found at:
> > http://www.energyplus.gov
> > 
> > The group web site is:
> > http://groups.yahoo.com/group/EnergyPlus_Support/
> > 
> > Attachments are not allowed -- please post any files to the 
appropriate folder
> > in the Files area of the Support Web Site.
> > 
> > EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf 
under the
> > Documentation link and press the "search" button.
> > 
> > Yahoo! Groups Links
> > 
> > 
> > 
> > 
> > 
> 
> 
> ========================================================
> Michael J. Witte, GARD Analytics, Inc.
> EnergyPlus Testing and Support      
> EnergyPlus-Support@...
>




The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/