[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

Re: [EnergyPlus_Support] purchased air problem....



Thank you very mutch. There was an error before theese errors.
  

"Michael J. Witte" <mjwitte@xxxxxxxx> wrote:
          Also, you may find it easier to use COMPACT HVAC:ZONE:PURCHASED AIR. See 
example file CompactHVAC-5ZonePurchAir.idf.

On 24 Apr 2007 at 3:35, kostas ordoumpozanis wrote:

> Hi I am new to energy plus and I have a proble with purchased air. I am
> following the example from file purchairtables.idf and i get the following
> errors...
> 
> Any ideas ?
> 
> This is the erros
> 
> ** Severe ** Node Connection Error, Node="NODE_1", ZoneInlet node did not
> find an outlet node.
> ** ~~~ ** Reference Object=CONTROLLED ZONE EQUIP CONFIGURATION,
> Name=HOME1 ** Severe ** Node Connection Error, Node="NODE_2", ZoneInlet node
> did not find an outlet node. ** ~~~ ** Reference Object=CONTROLLED ZONE
> EQUIP CONFIGURATION, Name=HOME2 ** Severe ** Node Connection Error,
> Node="NODE_3", ZoneInlet node did not find an outlet node. ** ~~~ **
> Reference Object=CONTROLLED ZONE EQUIP CONFIGURATION, Name=HOME3 ** Severe 
> ** Node Connection Error, Node="NODE_4", ZoneInlet node did not find an
> outlet node. ** ~~~ ** Reference Object=CONTROLLED ZONE EQUIP
> CONFIGURATION, Name=HOME4 ** Severe ** Node Connection Error, Node="NODE_5",
> ZoneInlet node did not find an outlet node. ** ~~~ ** Reference
> Object=CONTROLLED ZONE EQUIP CONFIGURATION, Name=HOME5 ** Severe ** Node
> Connection Error, Node="NODE_6", ZoneInlet node did not find an outlet node.
> ** ~~~ ** Reference Object=CONTROLLED ZONE EQUIP CONFIGURATION,
> Name=HOME6 ** Severe ** Node Connection Error, Node="NODE_7", ZoneInlet node
> did not find an outlet node. ** ~~~ ** Reference Object=CONTROLLED ZONE
> EQUIP CONFIGURATION, Name=KLIMAKOSTASIO ************* There were 7 node
> connection errors noted.
> 
> This is the part from my input file
> 
> !- =========== ALL OBJECTS IN CLASS: NODE LIST ===========
> NODE LIST,
> Home 1 Inlets, !- Node List Name
> NODE_1; !- Node_ID_1
> NODE LIST,
> Home 2 Inlets, !- Node List Name
> NODE_2; !- Node_ID_1
> NODE LIST,
> Home 3 Inlets, !- Node List Name
> NODE_3; !- Node_ID_1
> NODE LIST,
> Home 4 Inlets, !- Node List Name
> NODE_4; !- Node_ID_1
> NODE LIST,
> Home 5 Inlets, !- Node List Name
> NODE_5; !- Node_ID_1
> NODE LIST,
> Home 6 Inlets, !- Node List Name
> NODE_6; !- Node_ID_1
> NODE LIST,
> Klimak Inlets, !- Node List Name
> NODE_7; !- Node_ID_1
> 
> 
> !- =========== ALL OBJECTS IN CLASS: CONTROLLED ZONE EQUIP CONFIGURATION
> =========== CONTROLLED ZONE EQUIP CONFIGURATION,
> Home1, !- Zone Name
> Home 1 Equipment, !- List Name: Zone Equipment
> Home 1 Inlets, !- Node List or Node Name: Zone Air Inlet Node(s) ,
> !- Node List or Node Name: Zone Air Exhaust Node(s)
> NODE_8, !- Zone Air Node Name NODE_9; !-
> Zone Return Air Node Name
> CONTROLLED ZONE EQUIP CONFIGURATION,
> Home2, !- Zone Name
> Home 2 Equipment, !- List Name: Zone Equipment
> Home 2 Inlets, !- Node List or Node Name: Zone Air Inlet Node(s) ,
> !- Node List or Node Name: Zone Air Exhaust Node(s)
> NODE_10, !- Zone Air Node Name NODE_11; !-
> Zone Return Air Node Name
> CONTROLLED ZONE EQUIP CONFIGURATION,
> Home3, !- Zone Name
> Home 3 Equipment, !- List Name: Zone Equipment
> Home 3 Inlets, !- Node List or Node Name: Zone Air Inlet Node(s) ,
> !- Node List or Node Name: Zone Air Exhaust Node(s)
> NODE_12, !- Zone Air Node Name NODE_13; !-
> Zone Return Air Node Name
> CONTROLLED ZONE EQUIP CONFIGURATION,
> Home4, !- Zone Name
> Home 4 Equipment, !- List Name: Zone Equipment
> Home 4 Inlets, !- Node List or Node Name: Zone Air Inlet Node(s) ,
> !- Node List or Node Name: Zone Air Exhaust Node(s)
> NODE_14, !- Zone Air Node Name NODE_15; !-
> Zone Return Air Node Name
> CONTROLLED ZONE EQUIP CONFIGURATION,
> Home5, !- Zone Name
> Home 5 Equipment, !- List Name: Zone Equipment
> Home 5 Inlets, !- Node List or Node Name: Zone Air Inlet Node(s) ,
> !- Node List or Node Name: Zone Air Exhaust Node(s)
> NODE_16, !- Zone Air Node Name NODE_17; !-
> Zone Return Air Node Name
> CONTROLLED ZONE EQUIP CONFIGURATION,
> Home6, !- Zone Name
> Home 6 Equipment, !- List Name: Zone Equipment
> Home 6 Inlets, !- Node List or Node Name: Zone Air Inlet Node(s) ,
> !- Node List or Node Name: Zone Air Exhaust Node(s)
> NODE_18, !- Zone Air Node Name NODE_19; !-
> Zone Return Air Node Name
> CONTROLLED ZONE EQUIP CONFIGURATION,
> Klimakostasio, !- Zone Name
> Klimak Equipment, !- List Name: Zone Equipment
> Klimak Inlets, !- Node List or Node Name: Zone Air Inlet Node(s) ,
> !- Node List or Node Name: Zone Air Exhaust Node(s)
> NODE_20, !- Zone Air Node Name NODE_21; !-
> Zone Return Air Node Name
> 
> !- =========== ALL OBJECTS IN CLASS: ZONE EQUIPMENT LIST ===========
> ZONE EQUIPMENT LIST,
> Home 1 Equipment, !- Name
> PURCHASED AIR, !- KEY--Zone Equipment Type 1
> Home 1 Purchased air, !- Type Name 1
> 1, !- Cooling Priority 1
> 1; !- Heating Priority 1
> ZONE EQUIPMENT LIST,
> Home 2 Equipment, !- Name
> PURCHASED AIR, !- KEY--Zone Equipment Type 1
> Home 2 Purchased air, !- Type Name 1
> 1, !- Cooling Priority 1
> 1; !- Heating Priority 1
> ZONE EQUIPMENT LIST,
> Home 3 Equipment, !- Name
> PURCHASED AIR, !- KEY--Zone Equipment Type 1
> Home 3 Purchased air, !- Type Name 1
> 1, !- Cooling Priority 1
> 1; !- Heating Priority 1
> ZONE EQUIPMENT LIST,
> Home 4 Equipment, !- Name
> PURCHASED AIR, !- KEY--Zone Equipment Type 1
> Home 4 Purchased air, !- Type Name 1
> 1, !- Cooling Priority 1
> 1; !- Heating Priority 1
> ZONE EQUIPMENT LIST,
> Home 5 Equipment, !- Name
> PURCHASED AIR, !- KEY--Zone Equipment Type 1
> Home 5 Purchased air, !- Type Name 1
> 1, !- Cooling Priority 1
> 1; !- Heating Priority 1
> ZONE EQUIPMENT LIST,
> Home 6 Equipment list, !- Name
> PURCHASED AIR, !- KEY--Zone Equipment Type 1
> Home 6 Purchased air, !- Type Name 1
> 1, !- Cooling Priority 1
> 1; !- Heating Priority 1
> ZONE EQUIPMENT LIST,
> Klimak Equipment , !- Name
> PURCHASED AIR, !- KEY--Zone Equipment Type 1
> Klimak Purchased air, !- Type Name 1
> 1, !- Cooling Priority 1
> 1; !- Heating Priority 1
> 
> !- =========== ALL OBJECTS IN CLASS: PURCHASED AIR ===========
> PURCHASED AIR,
> Home 1 Purchased air, !- Purchased Air Name
> NODE_1, !- Zone Supply Air Node Name
> 50, !- Heating Supply Air Temp {C}
> 13, !- Cooling Supply Air Temp {C}
> 0.02, !- Heating Supply Air Humidity Ratio
> {kg-H2O/kg-air} 0.02, !- Cooling Supply Air Humidity
> Ratio {kg-H2O/kg-air} NO LIMIT, !- heating limit autosize, 
> !- Maximum heating air flow rate {m3/s} NO LIMIT, 
> !- cooling limit autosize, !- Maximum cooling air flow rate
> {m3/s} NO OUTSIDE AIR, !- outside air autosize; !-
> Outside air flow rate {m3/s}
> PURCHASED AIR,
> Home 2 Purchased air, !- Purchased Air Name
> NODE_2, !- Zone Supply Air Node Name
> 50, !- Heating Supply Air Temp {C}
> 13, !- Cooling Supply Air Temp {C}
> 0.02, !- Heating Supply Air Humidity Ratio
> {kg-H2O/kg-air} 0.02, !- Cooling Supply Air Humidity
> Ratio {kg-H2O/kg-air} NO LIMIT, !- heating limit autosize, 
> !- Maximum heating air flow rate {m3/s} NO LIMIT, 
> !- cooling limit autosize, !- Maximum cooling air flow rate
> {m3/s} NO OUTSIDE AIR, !- outside air autosize; !-
> Outside air flow rate {m3/s}
> PURCHASED AIR,
> Home 3 Purchased air, !- Purchased Air Name
> NODE_3, !- Zone Supply Air Node Name
> 50, !- Heating Supply Air Temp {C}
> 13, !- Cooling Supply Air Temp {C}
> 0.02, !- Heating Supply Air Humidity Ratio
> {kg-H2O/kg-air} 0.02, !- Cooling Supply Air Humidity
> Ratio {kg-H2O/kg-air} NO LIMIT, !- heating limit autosize, 
> !- Maximum heating air flow rate {m3/s} NO LIMIT, 
> !- cooling limit autosize, !- Maximum cooling air flow rate
> {m3/s} NO OUTSIDE AIR, !- outside air autosize; !-
> Outside air flow rate {m3/s}
> PURCHASED AIR,
> Home 4 Purchased air, !- Purchased Air Name
> NODE_4, !- Zone Supply Air Node Name
> 50, !- Heating Supply Air Temp {C}
> 13, !- Cooling Supply Air Temp {C}
> 0.02, !- Heating Supply Air Humidity Ratio
> {kg-H2O/kg-air} 0.02, !- Cooling Supply Air Humidity
> Ratio {kg-H2O/kg-air} NO LIMIT, !- heating limit autosize, 
> !- Maximum heating air flow rate {m3/s} NO LIMIT, 
> !- cooling limit autosize, !- Maximum cooling air flow rate
> {m3/s} NO OUTSIDE AIR, !- outside air autosize; !-
> Outside air flow rate {m3/s}
> PURCHASED AIR,
> Home 5 Purchased air, !- Purchased Air Name
> NODE_5, !- Zone Supply Air Node Name
> 50, !- Heating Supply Air Temp {C}
> 13, !- Cooling Supply Air Temp {C}
> 0.02, !- Heating Supply Air Humidity Ratio
> {kg-H2O/kg-air} 0.02, !- Cooling Supply Air Humidity
> Ratio {kg-H2O/kg-air} NO LIMIT, !- heating limit autosize, 
> !- Maximum heating air flow rate {m3/s} NO LIMIT, 
> !- cooling limit autosize, !- Maximum cooling air flow rate
> {m3/s} NO OUTSIDE AIR, !- outside air autosize; !-
> Outside air flow rate {m3/s}
> PURCHASED AIR,
> Home 6 Purchased air, !- Purchased Air Name
> NODE_6, !- Zone Supply Air Node Name
> 50, !- Heating Supply Air Temp {C}
> 13, !- Cooling Supply Air Temp {C}
> 0.02, !- Heating Supply Air Humidity Ratio
> {kg-H2O/kg-air} 0.02, !- Cooling Supply Air Humidity
> Ratio {kg-H2O/kg-air} NO LIMIT, !- heating limit autosize, 
> !- Maximum heating air flow rate {m3/s} NO LIMIT, 
> !- cooling limit autosize, !- Maximum cooling air flow rate
> {m3/s} NO OUTSIDE AIR, !- outside air autosize; !-
> Outside air flow rate {m3/s}
> PURCHASED AIR,
> Klimak Purchased air, !- Purchased Air Name
> NODE_7, !- Zone Supply Air Node Name
> 50, !- Heating Supply Air Temp {C}
> 13, !- Cooling Supply Air Temp {C}
> 0.02, !- Heating Supply Air Humidity Ratio
> {kg-H2O/kg-air} 0.02, !- Cooling Supply Air Humidity
> Ratio {kg-H2O/kg-air} NO LIMIT, !- heating limit autosize, 
> !- Maximum heating air flow rate {m3/s} NO LIMIT, 
> !- cooling limit autosize, !- Maximum cooling air flow rate
> {m3/s} NO OUTSIDE AIR, !- outside air autosize; !-
> Outside air flow rate {m3/s}
> 
> 
> Thank you 
> Odoumpozanis Kostas
> Kozani, Greece
> 24/04/2007
> 
> 
> ---------------------------------
> Ahhh...imagining that irresistible "new car" smell?
> Check outnew cars at Yahoo! Autos.
> 
> [Non-text portions of this message have been removed]
> 
> 
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
> 
> EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the
> Documentation link and press the "search" button.
> 
> Yahoo! Groups Links
> 
> 
> 
> 
> 



         

       
---------------------------------
Ahhh...imagining that irresistible "new car" smell?
 Check outnew cars at Yahoo! Autos.

[Non-text portions of this message have been removed]



The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/