The problem here is that COMPACT HVAC objects are still present in the idf
file. If you want to merge files so that two systems are serving the same
zone, you must run the simple single-system COMPACT HVAC simulation and use the
expidf output file to do the merging.
In this case, the approach would be to run a simulation with only fan coil
units using COMPACT HVAC, then take the expidf output file and merge in the
DOAS system.
Your present input file can be fixed as follows:
1. Run it, as you have already, and you will get fatal errors.
2. Take the expidf output file and rename it to a new filename.idf.
3. This file has 3 instances of CONTROLLED ZONE EQUIP CONFIGURATION and ZONE
EQUIPMENT LIST for Zone 25. Keep the ones named "25 Equipment" and delete the
others.
4. The file contains both a DIRECT AIR unit and a terminal reheat AIR
DISTRIBUTION UNIT. Keep one of these and delete the others, depending on what
type of system the DOAS is.
5. Add the DOAS terminal unit to ZONE EQUIPMENT LIST "25 Equipment" with
priority 1, and change the fan coil priorities to 2.
6. In the ZONE EQUIP CONFIGURATION object, you will also need to get the node
names adjusted. The return air node name must match the inlet to the ZONE
MIXER for the DOAS, and the zone inlets must now be a NODE LIST name, and the
NODE LIST will need to contain both the DOAS supply inlet to the zone and the
fan coil supply inlet.
7. If you use DIRECT AIR for the DOAS terminal unit, you will also need to
delete the hot water reheat coil and it's branch.
8. After all of this, you may need to make some other adjustments, but this
should get you closer to the final goal.
Mike
On 25 Apr 2007 at 11:20, love9787m wrote:
> Hello Mike
>
> Now, I'm making a model served DOAS plus fancoil uint.
> As your advice, merged the idf file with the DOAS description,
> add the DIRECT AIR unit to ZONE EQUIPMENT LIST.
> But This message showed below
>
> CONTROLLED ZONE EQUIP CONFIGURATION Zone Name, duplicate name=25
> ** ~~~ ** ..only one Controlled Zone Equip Configuration per
> zone is allowed.
> ** Severe ** CONTROLLED ZONE EQUIP CONFIGURATION List Name: Zone
> Equipment, duplicate name=ZONE25EQUIPMENT
> ** ~~~ ** ..another Controlled Zone is using that Zone Equipment
> List.
>
> Ana What is the correct means of merging?
> Please let me about problem.
>
> Thanks in advance your support.
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
>
> EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the
> Documentation link and press the "search" button.
>
> Yahoo! Groups Links
>
>
>
>
>
========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/