Re: [EnergyPlus_Support] Windowblinds
1. Use WindowShadingControl. There is also a field in the window object
(Surface:HeatTransfer:Sub) that attaches the control to a specific window(s).
2. The simplest way is to use VENTILATION. A more detailed approach is to use
AIRFLOWNETWORK:*.
Mike
On 27 Apr 2007 at 7:41, pezpapagallo wrote:
> Good morning, I have a question about windowblinds. How can I define
> some kind of blind or shading system that has to be closed durind the
> summer days?
>
> Another question that I want to ask, How can I define natural
> ventilation during nights by opening a window?
>
========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/