Re: [EnergyPlus_Support] Blinds between Glas - Block Beam Solar
Is this a venetian blind or diffusing shade?
What are the blind/shade thermal characteristics? Low conductivity
would reduce window heat gain.
When the blind/shade is deployed does it have a solar and/or visible
transmittance? If it is opaque to solar, but has visible transmittance
this would reduce transmitted solar, but still transmit daylight.
Rob
========
Arno Dentel wrote:
> Hello,
>
> I simulated a simple room with a window with integrated blinds (between
> glas).
> The control stragey for the shading device is: block beam solar.
> The outputs of the simulation seem to be not realistic.
> If the shading device is on, the transmitted solar energy in the room and
> the window heat gain
> are zero. Although the daylight in the zone is increasing?
> Has anybody an idea? Or is there an error in my input discription?
>
> Regards,
> Arno
>
> [Non-text portions of this message have been removed]
>
>
--
Robert J. Hitchcock, Ph.D.
Lawrence Berkeley National Laboratory
1 Cyclotron Road, Mailstop 90-3111
Berkeley, CA 94720
RJHitchcock@xxxxxxx
530.295.9433 (telecommute office)
[Non-text portions of this message have been removed]
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/