[EnergyPlus_Support] Re: One Wall Surface coupled with Several Surfaces



Option B works fine, thanks!

--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "Michael J. Witte"
<mjwitte@...> wrote:
>
> > You should define one wall in contact with the corridor for each
office. 
> 
> Or you can let the program do this for you automatically (new v2.0
feature):
> 
> 1.  In each office describe the wall next to the corridor using 
> "unenteredOtherZoneSurface" and specify the Corridor as the outside
face 
> environment object.
> 
> 2.  Do no describe any of these walls in the corridor zone - the 
> "unenteredOtherZoneSurface" option will create them internally.  You
can see 
> them in output reports, but you do not need to describe them in the
idf file.
> 
> Mike
> 
> 
> On 3 May 2007 at 3:54, Miguel Angel Pascual wrote:
> 
> > You should define one wall in contact with the corridor for each
office. 
> > 
> > ---
> > Miguel Angel Pascual Buisan
> > 
> > 
> > -----Original Message-----
> > From: "Jose Benitez" <joseb@...>
> > Date: Wed, 02 May 2007 19:53:27 
> > To:EnergyPlus_Support@xxxxxxxxxxxxxxx
> > Subject: [EnergyPlus_Support] One Wall Surface coupled with
Several Surfaces
> > 
> > Hi, I am doing a simulation that includes a corridor (a zone) that is
> >  the outside surface zone for several offices (each one a different
> >  zone). Do I need to fragment my corridor wall so it coincides
with the
> >  offices walls (so surfaces on the offices correspond to surfaces on
> >  the corridor)? or Can I define the surfaces in the offices with the
> >  wall on the corridor as their outside zone and jsut define one
wall on
> >  the corridor with "unenteredOtherZoneSurface"?
> > 
> > 
> > 
> > 
> > The primary EnergyPlus web site is found at:
> > http://www.energyplus.gov
> > 
> > The group web site is:
> > http://groups.yahoo.com/group/EnergyPlus_Support/
> > 
> > Attachments are not allowed -- please post any files to the
appropriate folder
> > in the Files area of the Support Web Site.
> > 
> > EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf
under the
> > Documentation link and press the "search" button.
> > 
> > Yahoo! Groups Links
> > 
> > 
> > 
> > 
> > 
> 
> 
> ========================================================
> Michael J. Witte, GARD Analytics, Inc.
> EnergyPlus Testing and Support      
> EnergyPlus-Support@...
>




The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/