Re: [EnergyPlus_Support] VAV Ventilation rate
To get a listing of all available report variables for a given input file, add
"report, variable dictionary;" to the input, run a simulation, and look in the
.rdd output file. For example file VAVSingleDuctReheat.IDF, the rdd output
includes these variables:
HVAC,Sum,Zone Mechanical Ventilation Total Volume of Outside Air [m3]
HVAC,Sum,Zone Mechanical Ventilation Total Mass of Outside Air [kg]
HVAC,Average,Zone Mechanical Ventilation Air Change Rate [ach]
These same variables should show in your rdd output file. Then add REPORT
VARIABLE objects to produce output for these values. For example:
REPORT VARIABLE, *, Zone Mechanical Ventilation Air Change Rate, hourly;
Mike
On 8 May 2007 at 2:45, love9787m wrote:
> Hi,
>
> Currently, Simulating the VAV system.
> To identify Ventilation rate and Air change rate per hour,
> I made mechanical Ventilation flow rate, air change rate.
> But I couldnot find those results. So i checked expfile and It also
> didn't have those results as well.
> why those results didn't show in VAVsystem
>
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
>
> EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the
> Documentation link and press the "search" button.
>
> Yahoo! Groups Links
>
>
>
>
>
========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/