Re: [EnergyPlus_Support] turn off chiller



You can specify a system availability manager for the chilled water plant loop. 
 See PLANT LOOP "Chilled Water Loop Secondary Water Loop" in example file 
IceStorage-Parallel.idf.

However, if free cooling (outside air economizer) is enough to meet the cooling 
load, this should not be necessary.  The cooling coil will not turn on and the 
chilled water loop will shut down (if the pump control is INTERMITTENT).

Mike


On 8 May 2007 at 3:41, thaisarquiteta wrote:

> Hello 
> 
> I'd like to know how could I turn off only the chiller equipment due 
> to outside air temperature. My objective is to turn off the chiller 
> but insuflate outside air, using the supply fan, whenever the 
> outside air temperature is ok for that (free-cooling/ mechanical 
> ventilation). 
> My chiller is a electric one, with air cooled condenser type.
> Using the system availability manager all the system is turned off, 
> including fans, causing the attached kind of problems.
> Would someone please help me???
> Thanks in advance,
> 
> Thais Aya H. Inatomi
> 
> 
> Program Version,EnergyPlus 1.4.0.025, 5/7/2007 11:42 PM,IDD_Version 
> 1.4.0.025
>    **   ~~~   ** Based on ASHRAE 55-2004 graph (Section 5.2.1.1)
>    **   ~~~   ** During DesignDay Environment [02/21 - 02/21]: 
> ANNUAL COOLING WB=MDB
>    **   ~~~   ** 12.0 hours were uncomfortable in zone: SPACE1-1
>    ** Warning ** Inside surface heat balance did not converge with 
> Max Temp Difference [C] =2.204E-003 vs Max Allowed Temp Diff [C] 
> =2.000E-003
>    **   ~~~   ** occuring in simulation=SAO_PAULO/CONGONHAS - BLZ 
> TMY3-837800 WMO#=837800 at 04/19 11:20
>    ** Warning ** Inside surface heat balance did not converge with 
> Max Temp Difference [C] =2.138E-003 vs Max 
> 
>  ** Warning ** Inside surface heat balance convergence problem 
> continues.....700
>    ** Warning ** Inside surface heat balance convergence problem 
> continues.....800
>    ** Severe  ** Temperature out of bounds (-169.04) for surface=C1-
> 1SUP
>    **   ~~~   ** in Zone=SUP-PLENUM-1
>    **   ~~~   ** occuring in environment=SAO_PAULO/CONGONHAS - BLZ 
> TMY3-837800 WMO#=837800 at 04/26 23:30
>    **   ~~~   ** A temperature out of bounds problem can be caused 
> by several things.  The user
>    **   ~~~   ** should check the weather environment, the level of 
> internal gains with respect
>    **   ~~~   ** to the zone, and the thermal properties of their 
> materials among other things.
>    **   ~~~   ** A common cause is a building with no thermal mass --
>  all materials with
>    **   ~~~   ** Regular-R definitions.
>    **  Fatal  ** EnergyPlus has exited due to the reason stated above
>    ************* EnergyPlus Terminated--Fatal Error Detected. 27 
> Warning; 1 Severe Errors
> 
> 
> 
> 
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
> 
> EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the
> Documentation link and press the "search" button.
> 
> Yahoo! Groups Links
> 
> 
> 
> 
> 


========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support      
EnergyPlus-Support@xxxxxxxx





The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/