[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]
[EnergyPlus_Support] EvapCooler RDD Special Cooler
To All,
I would like to simulate an indirect evaporative cooler where the
secondary air is building exhaust air - so I am using the RDDSpecial
object. I would like the object to behaive like a wet coil indirect
evaporative cooler. The issue I am having is that I can't figure out
what the inputs for the object should be to make it behaive like a wet
coil as opposed to a regular indirect pad cooler. I know there is an
example file, but I don't know what type of cooler is in the example
file. What should I input for the "Cooler Maximum Effectiveness"?
What about the "Dewpoint Effectiveness Factor"?
Thanks,
Andrew
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/