[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]
[EnergyPlus_Support] Re: Building Meets Design Day But Not Weather File?
Problem Solved.
It seems that this problem is caused by the fact that the design day
(7/21) for the south zones does not have the same sun exposure to the
zones as any day in the shoulder months. In fact, it is far less.
Therefore, when the building is exposed to the high solar heat gain
on the south zones during September and October, the HVAC system
cannot maintain temperature for these zones. I have solved this
problem by adding a second summer design day with a different date
(10/31) that has a higher solar heat gain for the south zones. This
seemed to do the trick. Now the south zones operate between the
setpoints.
--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "noelcrrl" <noelcrrl@...>
wrote:
>
> All-
>
> All-
>
> I have created a building model representing an office. The model
> meets the heating and cooling temperature setpoints, 70F and 75F
> respectively, for both the winter and summer design days, according
> to the ESO. However, when I run the weather file, the temperature
of
> the south zones cannot be maintained at setpoint and drift beyond
75F
> between 10am and 4pm during the shoulder months (i.e. September and
> October) consistently (on a daily basis). Has anyone ever
> encountered this problem in the past? What could be causing this?
> Thanks in advance for your help.
>
> Additional Info:
> Simulation takes place in Houston
> Occupancy (6am - 6pm)
> Fan Schedule (5am-6pm)
> Setback (6pm-5am) Temps: 55F (heating) and 90F (Cooling)
> Design Day-temps do not setback
>
> Noel
>
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/