[EnergyPlus_Support] Re: PTACs and Evaporative Cooling
--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "asheaffe" <sheaffer@...>
wrote:
>
> To All,
>
> Is it at all possible to insert an evaporative precooler upstream of a
> cooling coil in a Packaged Terminal Heat Pump?
>
> Thanks,
>
> Andrew
>
For your consideration: It makes no sense to use a direct evaporative
cooler in front of ANY refrigeration system. The evap cooler is just
an adiabatic device which transfers sensible heat to latent; any
refrigeration system will have to remove exactly the same amount of
energy with the evap cooler in place as without. Of course, an
INdirect evap cooler will provide useful assistance to a refrigeration
system as a pre-cooler.
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/