Re: [EnergyPlus_Support] shading device(slat-type) perpendicular to building surface
1. This would have to be constructed from a set of
Surface:Shading:Detached:Building objects.
2. Wind-driven airflow can be modeled one of two ways, with simple VENTILATION
or INFILTRATION objects, or with the more complex AirFlowNetwork objects. If
you use the airflownetwork approach, you will need to set the window
ventilation controls to force the window to be open at all times. EnergyPlus
will not be able to calculate the airflow resistance of the shading device.
You will need some other way to determine the flow characteristics outside of
EnergyPlus.
Mike
On 2 Jun 2007 at 8:00, neslihanturkmenoglu wrote:
> -How can I define slat type shading device(slats perpendicular and
> parallel to wall surface) perpendicular to building surface?
>
> -My window is open. I will search the effects of shading devices on
> cooling loads by considering solar transmittance and airflow
> transmittances of these devices at the same time. So if I have to
> define a glazing for window with the values of 0.99999 and
> reflectances 0.00001, how will the program consider airflow
> transmittances as the window is closed. Is there an other way for
> simulating this situation?
>
>
> I am looking forward to your answer
>
> thank you very much
>
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
>
> EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the
> Documentation link and press the "search" button.
>
> Yahoo! Groups Links
>
>
>
>
>
========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/