[EnergyPlus_Support] Issue about Variable Speed Pump when minimum flow rate is set
Dear Supporter,
I met one issue about Variable Speed Pump when I tried to set its
minimum flow rate. I used the sample idf file - 5ZoneAirCooled.idf
and two EnergyPlus versions: 1-4-0 and 2-0-0. When the Min Flow Rate
of CW Circ Pump (a Variable Speed Pump) is 0, the flow rate of this
pump changes every hour, according to the building cooling load. But
when I set the Min Flow Rate to 0.35, the flow rate of this pump
keeps as constant as its maximum value in 99% cooling time. I post
part of this result (EnergyPlus Version 1-4-0) at June 26th.
Flow rate when Min as 0 Flow rate when Min as 0.35
7:00 0.105827619 1.350900891
8:00 0.135507546 1.350900891
9:00 0.178759363 1.350900891
10:00 0.302383865 1.350900891
11:00 0.420776425 1.350900891
12:00 0.418370539 1.350900891
13:00 0.343836121 1.350900891
14:00 0.467934478 1.350900891
15:00 0.567593695 1.350900891
16:00 0.617053734 1.350900891
17:00 0.510519396 1.350900891
18:00 0.412040288 1.350900891
19:00 0.21313587 1.350900891
20:00 0.197417633 1.350900891
Best regards
Qingfan
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/