Re: [EnergyPlus_Support] Internal Radiant Heat Distribution
This is discussed briefly in the Engineering Reference under "Inside Heat
Balance" (beginning on p. 47, pdf p. 83). There are no report variables for
the LW or visible radiant flux at a surface. I suppose you could observe the
effect of this flux by reporting Surface Inside Temperature with and without
the internal gain present.
Mike
On 13 Jun 2007 at 17:54, Micheal wrote:
> I am working on a simple single room single zone building with no
> windows and purchased air. Also, I have some internal equipment load
> but no latent heat. It seems as if EPlus sums total internal load
> convective heat gain with convection heat gain to air of the other
> surfaces to produce Purchased Air Sensible Cooling variable.
>
> My question is about the internal radiant heat gain. I would guess
> that this heat would be distributed over the inside surfaces of the
> model in some way. The problem is that I do not see an inside surface
> variable for radiant heat to verify this. Any suggestion or comments
> would be appreciated.
>
> I could upload my model if you would like to see specifics.
>
> Thanks,
> Mike
>
> PS: I have looked through the Manuals but have not found an answer to
> this in them.
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
>
> EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the
> Documentation link and press the "search" button.
>
> Yahoo! Groups Links
>
>
>
>
>
========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/