Re: [EnergyPlus_Support] ideal cooling + constVolSystem
In the ZONE EQUIPMENT LIST objects the "priority" is the order in which the
equipment is simulated. Because the impact of the outside air can change the
net heating or cooling load required, it should always be simualted first. So,
change the heating and cooling priority for the DIRECT AIR units to be 1, and
adjust the other equipment prioirities accordingly. This should solve the
problem.
Mike
On 19 Jun 2007 at 10:08, Sebastian Dietz wrote:
> Hello everybody
>
> currently I'm modelling a building with 10 zones. Each zone gets heated
> by a basebord and is served with outside air by a constant volume
> System. Up to here the system runs quite good. Now I want to model a
> ideal cooling System to limit the maximal indoor temperature. Thus I
> used the Object "PurchasedAir", in order to provide cool air for each
> Zone. But I get miximum iterations Warnings for each timestep. I changed
> the values for tolerances with no effect.
> Does anybody know, how to solve the problem, or is there another easy
> way to model an ideal cooling system.
> For more information I uploaded my "Typgebaeude.idf" file
>
> Thanks in advance
> Sebastian
>
> --
> Sebastian Dietz
> Fraunhofer-Institut for Solare Energiesysteme ISE
> Heidenhofstrasse 2, 79110 Freiburg, Germany
> Phone: +49 (0) 7 61/ 45 88-51 36
> Sebastian.Dietz@xxxxxxxxxxxxxxxxx
> http://www.ise.fraunhofer.de
> -------------------------------------------
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
>
> EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the
> Documentation link and press the "search" button.
>
> Yahoo! Groups Links
>
>
>
>
>
========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/