[EnergyPlus_Support] EnergyPlus validation not working. Help
We've been getting results for E+ that we found suspicious,
particularly with surface reflectivity, so we attempted to do a simple
real world validation for Energyplus using an simple solar box (a
thermal equivalent of the 3D rendering Cornell box). 
For the solar box, we used a solar box cooker with reflective panels.
In EnergyPlus we made the same R10 2' square insulated box with a
single clear glass window and used 100% reflective glazing for
reflectors (since E+ doesn't let you specify specularity on normal
materials - please change!).
We ran it on a clear sky solar date at the same tilt. Peak temp results:
Real Solar Box: 350 F
Hand calculated result: 360 F
EnergyPlus: 210 F
EnergyPlus (Finite Differencing): 117F
If i delete the reflectors, the solar gain changes only a tiny amount
and the box temperatures don't change - obviously the reflection is
not working properly - any ideas? (yes full interior/exterior with
reflections is turned on)
The second question is what is up with Finite Differencing? 
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
 
Yahoo! Groups Links
<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
    Individual Email | Traditional
<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)
<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/