[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

Re: [EnergyPlus_Support] A question about sky temperature



As noted earlier in this group (available by searching at the yahoo 
group site):

It uses the Horizontal IR from sky as a basis (we calculate this on
the weather files and design days)

          ! Calculate sky temperature, use IRHoriz if not missing
          IF (IRHoriz == "missing") THEN
!         Missing, use sky cover
            OSky=OpaqueSkyCover
            TDewK=MIN(DryBulb,DewPoint)+TKelvin
            ESky= (.787 +.764*LOG((TDewK)/TKelvin))*
                              (1. + .0224*OSky - 0.0035*(OSky**2) + 
.00028*(OSky**3))
            SkyTemp=(DryBulb+TKelvin)*(ESky**.25)-TKelvin
          ELSE  ! Valid IR from Sky
            SkyTemp=(IRHoriz/Sigma)**.25 -TKelvin
          ENDIF

Sky IR is calculated as:
         ! Determine Sky Temp ==>
         ! Function of DryBulb, DewPoint, OpaqueSkyCover
         ! Calculate Sky IR
         !HIR = ESKY * SIGMA * (TOUT**4)
         !
         !where
         !
         !HIR = horizontal IR intensity (W/m2)
         !ESKY = sky emissivity
         !SIGMA = Stefan-Boltzmann constant = 5.6697e-8 W/m2-K4
         !TOUT = drybulb temperature (K)
         !
         !The sky emissivity is given by
         !
         !ESKY = [0.787 + 0.764*ln(TDEW/273)]*
                      [1 + 0.0224*N - 0.0035*(N**2) + 0.00028*(N**3)]
         !
         !where
         !
         !TDEW = dewpoint temperature (K)
         !N = opaque sky cover (tenths)
         !
         !Example: Clear sky (N=0), TOUT = 273+20=293K, TDEW = 273+10=283K:
         !
         !ESKY = 0.787 + 0.764*0.036 = 0.815
         !HIR = 0.815*5.6697e-8*(293**4) = 340.6 W/m2

         !References:
         !
         !George N. Walton, "Thermal Analysis Research Program 
Reference Manual,"
         !NBSIR 83-2655, March 1983, p. 21.
         !
         !G. Clark and C. Allen, "The Estimation of Atmospheric 
Radiation for Clear and
         !Cloudy Skies," Proc. 2nd National Passive Solar Conference 
(AS/ISES), 1978, pp. 675-678.



At 01:17 AM 6/25/2007, wanglei wrote:
>   After reading the document of InputOutputReference, we can know 
> the sky temperature is calculated using the flowing formula:
>   sky Temperature=power((Horizontal IR/SigMa),0.25)-273.15
>who can give me the more detail literatures about how to define the 
>value of  Horizontal IR and calculate the sky temperature.

Linda

EnergyPlus WebSite: http://www.energyplus.gov
Owner: EnergyPlus_Support list
Member: EnergyPlus Development Team



[Non-text portions of this message have been removed]



The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/