The desiccant regen coil cannot be autosized.  The error message indicates that 
the coil size needs to be at least 7712.001543[W], and the coil is not 
delivering any heating (either because it is scheduled off or its capacity is 
zero).  Specify a size on the regen coil object that is 7713[W] or greater.

Mike


On 3 Jul 2007 at 8:00, love9787m wrote:

> Hi,
> 
> To control the indoor latent cooling load, I've modified some object.
> and changed the value to autosizing.
> After finised modification of model, 
> The error message has appeared below 
> 
> Inadequate heat delivered by desiccant regen coil - RESULTS INVALID! 
> Check regen coil capacity and schedule.
>    ** This error occurred 5773 times.
>    ** DESICCANT DEHUMIDIFIER:SOLID=DESICCANT 1
>    ** Load requested [W] from COIL:GAS:HEATING=DESICCANT REGEN COIL
>    ** Max=7712.001543
>    ** Load request exceeded delivered by [W]
>    ** Max=7712.001543
> 
> what is the problem? How can I handle this problem?
> 
> 
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
> 
> EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the
> Documentation link and press the "search" button.
> 
> Yahoo! Groups Links
> 
> 
> 
> 
> 


========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support      
EnergyPlus-Support@xxxxxxxx





The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/