[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

Re: [EnergyPlus_Support] ideal cooling + constVolSystem



I will submit the suggestion to add an exhaust node to Purchase Air.  The best 
suggestion I can make at this point is to use COMPACT HVAC:ZONE:FAN COIL with 
COMPACT HVAC:PLANT:* objects to create the fan coil systems and the required 
plant loops.  You can add this to your existing idf file, but it will not run, 
because it will create conflicting CONTROLLED ZONE EQUIP CONFIGURATION and ZONE 
EQUIPMENT LIST objects.  You will need to take the expidf file and edit it by 
hand to delete the extra zone equipment objects and add the fan coil units to 
the zone equipment lists.

Mike


On 3 Jul 2007 at 16:39, Sebastian Dietz wrote:

> Hello Mike,
> 
> we are still dealing with the problem to combine ideal cooling with an 
> Air Loop. It seems, that the only way to get the required cooling energy 
> of a zone is to use a window ac - or a fan coil object. These are 
> achievable systems, but needs a lot of work to model. Especially if it 
> is a large building it is really time consuming.
> It would be nice, if you know (or your expert) an easeir way to model 
> such a system. If not, it would be a good improvement to modify the 
> purchased air object for the next release of EnergyPlus.
> 
> Thanks for your help
> best regards
> 
> sebastian
> 
> 
> 
> Michael J. Witte schrieb:
> > I think I see the problem now.  At the zone level EnergyPlus tries to balance
> > airflows.  The airflow on the return air node is equal to the sum of inlet
> > flows less exhaust node flows.  Because Purchased Air only places flow on an
> > inlet node, the zone air balance does not see a corresponding flow at an
> > exhaust node.  This is causing a flow at the return node that does not balance
> > with the rest of the air loop.  So, it appears that you cannot combine
> > Purchased Air with an air loop serving the same zone.  
> >
> > I will ask the air loop expert if there is a way to make this work, but I
> > suspect you will need to use a piece of zone equipment (fan coil, window ac,
> > ptac) to provide cooling.
> >
> > Mike
> >
> >
> > On 22 Jun 2007 at 17:31, Sebastian Dietz wrote:
> >
> >   
> >> Dear Mike,
> >>
> >> the max iteration errors occur only if I run the simulation with air 
> >> loop system in combination with the purchased air object. When I turn 
> >> off the purchased air the System runs fine. So it seems, that the 
> >> problem is the use of both. I chanced your suggestions, but the max 
> >> iteration errors are sitll the same.
> >>
> >> best regards
> >> sebastian
> >>
> >> Michael J. Witte schrieb:
> >>     
> >>> I tried turning off the air loop system and the max iteration errors went
> >>> away. 
> >>>  So the problem is in that part of the simulation.
> >>>
> >>> I see that most (or all) of the air loop components are autosized, and all
> >>> but one of the DIRECT AIR units has a hard number for flow rate (not
> >>> autosized). The autosizing algorithm will not see the flow rates in the
> >>> DIRECT AIR objects. 
> >>>  If you want to force a certain flow rate for a terminal unit, you must
> >>>  enter 
> >>> this in the ZONE SIZING object.  In the ZONE SIZING objects, add these
> >>> fields:
> >>>
> >>> ZONE SIZING,
> >>>
> >>>     flow/zone,                        !- cooling design air flow method 0.7,
> >>>                            !- cooling design air flow rate {m3/s}
> >>>
> >>> For each zone, specify the desired flow rate here.  This should result in an
> >>> air loop where all the flow rates are consistent and it should get rid of
> >>> the max iteration errors.
> >>>
> >>> Mike
> >>>
> >>>
> >>> On 20 Jun 2007 at 10:28, Sebastian Dietz wrote:
> >>>
> >>>   
> >>>       
> >>>> Hello Mike,
> >>>> please disregard my last mail.
> >>>> The iteration warnings still appear. I changed the priorities in  the ZONE
> >>>> EQUIPMENT LIST Objects, but it didn´t solve the Problem. Furthermore I
> >>>> increased the number of maximum iterations with no result. It would be
> >>>> nice, if you have another suggestion. I spent a lot of time on that problem
> >>>> and I`m stuck.
> >>>>
> >>>> thanks in advance
> >>>> sebastian
> >>>>
> >>>> Michael J. Witte schrieb:
> >>>>     
> >>>>         
> >>>>> In the ZONE EQUIPMENT LIST objects the "priority" is the order in which
> >>>>> the equipment is simulated.  Because the impact of the outside air can
> >>>>> change the net heating or cooling load required, it should always be
> >>>>> simualted first. So, change the heating and cooling priority for the
> >>>>> DIRECT AIR units to be 1, and adjust the other equipment prioirities
> >>>>> accordingly.  This should solve the problem.
> >>>>>
> >>>>> Mike
> >>>>>
> >>>>>
> >>>>> On 19 Jun 2007 at 10:08, Sebastian Dietz wrote:
> >>>>>
> >>>>>   
> >>>>>       
> >>>>>           
> >>>>>> Hello everybody
> >>>>>>
> >>>>>> currently I'm modelling a building with 10 zones. Each zone gets heated
> >>>>>> by a basebord and is served with outside air by a constant volume System.
> >>>>>> Up to here the system runs quite good. Now I want to model a ideal
> >>>>>> cooling System to limit the maximal indoor temperature. Thus I used the
> >>>>>> Object "PurchasedAir", in order to provide cool air for each Zone. But I
> >>>>>> get miximum iterations Warnings for each timestep. I changed the values
> >>>>>> for tolerances with no effect. Does anybody know, how to solve the
> >>>>>> problem, or is there another easy way to model an ideal cooling system.
> >>>>>> For more information I uploaded my "Typgebaeude.idf" file
> >>>>>>
> >>>>>> Thanks in advance
> >>>>>> Sebastian
> >>>>>>
> >>>>>> --
> >>>>>> Sebastian Dietz
> >>>>>> Fraunhofer-Institut for Solare Energiesysteme ISE
> >>>>>> Heidenhofstrasse 2, 79110 Freiburg, Germany
> >>>>>> Phone: +49 (0) 7 61/ 45 88-51 36
> >>>>>> Sebastian.Dietz@xxxxxxxxxxxxxxxxx
> >>>>>> http://www.ise.fraunhofer.de
> >>>>>> -------------------------------------------
> >>>>>>
> >>>>>>
> >>>>>>
> >>>>>> The primary EnergyPlus web site is found at:
> >>>>>> http://www.energyplus.gov
> >>>>>>
> >>>>>> The group web site is:
> >>>>>> http://groups.yahoo.com/group/EnergyPlus_Support/
> >>>>>>
> >>>>>> Attachments are not allowed -- please post any files to the appropriate
> >>>>>> folder in the Files area of the Support Web Site.
> >>>>>>
> >>>>>> EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the
> >>>>>> Documentation link and press the "search" button.
> >>>>>>
> >>>>>> Yahoo! Groups Links
> >>>>>>
> >>>>>>
> >>>>>>
> >>>>>>
> >>>>>>
> >>>>>>     
> >>>>>>         
> >>>>>>             
> >>>>> ========================================================
> >>>>> Michael J. Witte, GARD Analytics, Inc.
> >>>>> EnergyPlus Testing and Support      
> >>>>> EnergyPlus-Support@xxxxxxxx
> >>>>>
> >>>>>
> >>>>>
> >>>>>
> >>>>>   
> >>>>>       
> >>>>>           
> >>>> -- 
> >>>> Sebastian Dietz
> >>>> Fraunhofer-Institut for Solare Energiesysteme ISE
> >>>> Heidenhofstrasse 2, 79110 Freiburg, Germany
> >>>> Phone: +49 (0) 7 61/ 45 88-51 36
> >>>> Sebastian.Dietz@xxxxxxxxxxxxxxxxx
> >>>> http://www.ise.fraunhofer.de
> >>>> -------------------------------------------
> >>>>
> >>>>
> >>>>
> >>>> The primary EnergyPlus web site is found at:
> >>>> http://www.energyplus.gov
> >>>>
> >>>> The group web site is:
> >>>> http://groups.yahoo.com/group/EnergyPlus_Support/
> >>>>
> >>>> Attachments are not allowed -- please post any files to the appropriate
> >>>> folder in the Files area of the Support Web Site.
> >>>>
> >>>> EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the
> >>>> Documentation link and press the "search" button.
> >>>>
> >>>> Yahoo! Groups Links
> >>>>
> >>>>
> >>>>
> >>>>
> >>>>
> >>>>     
> >>>>         
> >>> ========================================================
> >>> Michael J. Witte, GARD Analytics, Inc.
> >>> EnergyPlus Testing and Support      
> >>> EnergyPlus-Support@xxxxxxxx
> >>>
> >>>
> >>>
> >>>
> >>>   
> >>>       
> >> -- 
> >> Sebastian Dietz
> >> Fraunhofer-Institut for Solare Energiesysteme ISE
> >> Heidenhofstrasse 2, 79110 Freiburg, Germany
> >> Phone: +49 (0) 7 61/ 45 88-51 36
> >> Sebastian.Dietz@xxxxxxxxxxxxxxxxx
> >> http://www.ise.fraunhofer.de
> >> -------------------------------------------
> >>
> >>
> >>
> >> The primary EnergyPlus web site is found at:
> >> http://www.energyplus.gov
> >>
> >> The group web site is:
> >> http://groups.yahoo.com/group/EnergyPlus_Support/
> >>
> >> Attachments are not allowed -- please post any files to the appropriate
> >> folder in the Files area of the Support Web Site.
> >>
> >> EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the
> >> Documentation link and press the "search" button.
> >>
> >> Yahoo! Groups Links
> >>
> >>
> >>
> >>
> >>
> >>     
> >
> >
> > ========================================================
> > Michael J. Witte, GARD Analytics, Inc.
> > EnergyPlus Testing and Support      
> > EnergyPlus-Support@xxxxxxxx
> >
> >
> >
> >
> >   
> 
> 
> -- 
> Sebastian Dietz
> Fraunhofer-Institut for Solare Energiesysteme ISE
> Heidenhofstrasse 2, 79110 Freiburg, Germany
> Phone: +49 (0) 7 61/ 45 88-51 36
> Sebastian.Dietz@xxxxxxxxxxxxxxxxx
> http://www.ise.fraunhofer.de
> -------------------------------------------
> 
> 
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
> 
> EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the
> Documentation link and press the "search" button.
> 
> Yahoo! Groups Links
> 
> 
> 
> 
> 


========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support      
EnergyPlus-Support@xxxxxxxx





The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/