Re: [EnergyPlus_Support] Question on CoolingCoil error message
The errors mean that the face area of the coil is too small for the volume flow
rate across the coil. In the COIL:Water:DetailedFlatCooling objects, are you
setting this field to autosize?
autosize, !- Minimum Air Flow Area {m2}
Other fields which may cause this problem are Number of Tube Rows and Number
of Tubes per Row.
Mike
On 23 Jul 2007 at 6:30, love9787m wrote:
> Currently running the simulation on DOAS with Pakaged Terminal Heat
> Pump, The center Zone of the building is served by DOAS and Out Zone
> (parameter Zone) is served by Packaged Terminal Heat Pump.
> At first, The simulation of building served by VAVsystem is successful.
> But second simulation model doesn't work due to those problem below.
> I've already adusted capacity of DETAILED COOLING COIL to autosizing.
> Above all, I really don't know fatal error what it is.
> I'm so tried of this repeated problem
>
> ** Warning ** COIL:Water:DetailedFlatCooling in Coil =DETAILED COOLING
> COIL
> ** ~~~ ** Air Flow Rate Velocity has greatly exceeded upper
> design guidelines of ~2.5 m/s
> ** ~~~ ** Air MassFlowRate[kg/s]=55.429247
> ** ~~~ ** Air Face Velocity[m/s]=NAN
> ** ~~~ ** Approximate MassFlowRate limit for Face Area[kg/s]=NAN
> ** ~~~ ** COIL:Water:DetailedFlatCooling could be
> resized/autosized to handle capacity
> ** Fatal ** Variable Z (NAN) out of range [0.0,1.0] in
> CalculateEpsFromNTUandZ
>
> Please let me know the method of this problem.
>
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
>
> EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the
> Documentation link and press the "search" button.
>
> Yahoo! Groups Links
>
>
>
>
>
========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/